    Hi
    Is it OK to use a 480/600VAC transformer to convert 380VAC to 480VAC ? The ratio is almost the same, is the transformer will react the same will lower voltage on the primary side ?
    Thanks,
    Hugo
  2. #2
    Join Date
    Feb 2003
    Wisconsin
    Posts
    4,354
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hublanc View Post
    Hi
    Thanks,
    Hugo
    Who manufactured the transformer? Did you call the transformer manufacturer? Can you post a picture of the name plate which should show the taps and connections? What is the KVA?
    With the very limited information that you have provide which was limited it the pri and sec voltage ration of the transformer in question it is almost if you are asking a question to get the answer that you want to hear which would be yes. BUT I would be reluctant to give an answer because there may be something that would say the contrary.
  3. #3
    Join Date
    Nov 2012
    India
    Posts
    409
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hi
    Thanks,
    Hugo
    1)The output voltage would be less a bit.
    2)The transformer capacity would reduce by almost 20%
  4. #4
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,447
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Hi
    Thanks,
    Hugo
    Is it all 60 Hz? Some transformers don't care much 50/60 Hz, others may. Best bet is to look at the nameplate and see what it says or just call the manufacturer and ask.
    Bob
  5. #5
    Join Date
    Apr 2008
    Ann Arbor, Michigan
    Posts
    7,861
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    151015-0739 EDT
    hublanc:
    If frequency is the same, then any transformer can be operated at any voltage below its rating. But you must stay within the current ratings of the windings. Also with some core materials (not standard transformer iron) there may be some performance problems at very low voltages. There is no heating problem at low voltage if you stay within the current ratings of the windings.
    If the frequency is different, then maximum continuous input voltage is (original rated voltage) * (new frequency)/(rated frequency). So as frequency goes down so must the voltage.
    Basically the maximum volt-time integral has to be constant to prevent severe saturation of the core. Most transformers are designed to go somewhat into saturation each cycle. This is to achieve maximum power capability with the minimum amount of iron and copper.
    Volt-time integral is the summation of all the short time (volt)*(small time increment) values per cycle.
    If you go higher in frequency than the rated frequency, then other factors create limitations.