    Quote Originally Posted by jonathankpa View Post
    Electrical engineer here - question on my own home for a change. Newer home, with a 3-way switch-controlled receptacle in one room. Over Christmas my wife unplugged the lamp that was being used on the recept, and plugged in some LED lights. We noticed that when the switch was off, they still lit (dimly). Finally got around to metering the receptacle today: 123 volts when the switch is on (OK). However, still 51.4 volts when the switch is off. Standard outlet tester indicates (red light off / 2 yellow lights on) that the outlet is ok from that standpoint. Thoughts on what to do / where to start 'troubleshooting'? I'm hoping this isn't a wiring issue. I'm a handyman also, but typically prefer projects by choice! Thanks in advance.

    If the romex was stapled too hard or pinched the voltage could be coming fromhot feeding the switch if it's in the same cable. If it's a switch loop that's most likely the cause

  2. #22
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    20,299
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    If the source is capacitive coupling in the traveler section of wire the observed results should not depend on which switch combination is used. If there is leakage across one contact pair in one switch then reversing both switches should cause a different result.

  3. #23
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    7,795
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    160127-1431 EST

    jonathankpa:

    Your meter is a high input impedance meter with an apparent input resistance of 10 mrgohm.

    Making current measurements in the amp or mA range can be a problem if the current is much greater than expected. A meter current protective fuse is typically in the range of $15. So use a resistor and the meter in volt mode. I suspect your current is less than 5 mA. Use a 1k 1/4 or 1/2 W resistor as a current shunt. 1 mA = 1 V.

    Measure the short circuit from your hot socket terminal when that terminal is de-energized. Measure the current for both switch positions that make the socket terminal off. Do the open circuit voltage measurement for both combinations.

    I will guess at between 0.02 to 2 mA for shoprt circuit current. Next determine the phase angle of the current relative to the voltage waveform of your 120 V source.

    .

  4. #24
    Join Date
    Jul 2014
    Location
    Washington State, USA
    Posts
    97
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    If you'll be doing routine work with power circuits

    A tool to get is a low-impedance solenoid meter, colloquially a "wiggy". If you won't be doing routine work with power circuits, hey, it's still an excuse to buy a new tool :-)

    Builder-grade components are the bottom of the quality ladder. Spec-grade replacements for the switches are much cheaper than your time is. Swap out the switches and you solve the noise problem at the same time.
    Last edited by Curious nerd; 01-27-16 at 05:17 PM. Reason: Restore line breaks

  5. #25
    Join Date
    Jan 2011
    Location
    Pennsylvania, USA
    Posts
    51
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    If the source is capacitive coupling in the traveler section of wire the observed results should not depend on which switch combination is used. If there is leakage across one contact pair in one switch then reversing both switches should cause a different result.
    Understanding you mean switching (toggling) both switches? We tried all 4 combinations of both switches. Both combinations yielding "off" were 51.4 volts. Both combinations yielding "on" were 120V.

  6. #26
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    20,299
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jonathankpa View Post
    Understanding you mean switching (toggling) both switches? We tried all 4 combinations of both switches. Both combinations yielding "off" were 51.4 volts. Both combinations yielding "on" were 120V.
    That makes it less likely that the problem is a switch with leakage unless it is leakage between the two traveler terminals rather than between the common terminal and one traveler terminal.

  7. #27
    Join Date
    Feb 2006
    Location
    Jersey
    Posts
    2,499
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    ??? Both switches still have commons.

    Remove the switches and go hard wire to hard wire. See what you get.
    " I'm at a crucial part of my painting "...........Monika Danneman

  8. #28
    Join Date
    Feb 2006
    Location
    Jersey
    Posts
    2,499
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    That makes it less likely that the problem is a switch with leakage unless it is leakage between the two traveler terminals rather than between the common terminal and one traveler terminal.
    Commons. Back stabbed. Maybe.
    Either way the op has to do something and not just keep taking meaurements.

    Rule out the switches first.
    " I'm at a crucial part of my painting "...........Monika Danneman

  9. #29
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    7,795
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    160127-2014 EST

    jonathankpa:

    I will make a wild guess that the wiring distance between your two switches is about 15 to 30 ft (I could guess this because the wiring is in a house, but that is not how I came to that conclusion.), and your short circuit current is about 5 to 25 microamperes as measured by your meter. I calculate 18 ft of wire, but that has potential for a lot of error.

    A problem at the levels you are measuring is that the actual meter input impedance is not just 10 megohms of resistance.

    .

  10. #30
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    7,795
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    160127-2053 EST

    ritelec:

    I don't believe there is anything wrong with his switches or wiring.

    A "wiggy" or the voltage across a 25 W incandescent will read essentially 0 V.

    .