User Tag List
Results 1 to 6 of 6
Thread: Home Inspector and bonding CSST
  1. #1
    Join Date
    Feb 2007
    Alexandria, VA
    Posts
    454
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I had a home inspector question my bonding of the CSST gas line. I bonded to the copper main water line within 2 feet of the entrance. He said he was not convinced it was properly bonded because the water line could change to plastic after it left the house, perhaps, somewhere between the house and the street.
    I did not have a convincing response for him. I just told him that I bonded it properly and there is only so much that a guy can do?
  2. #2
    Join Date
    May 2016
    Pavilion
    Posts
    2
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    nfpa54 (fuel gas) 2008 requires a #6 copper from the closest point of entry of the black pipe into the home back to the panel. if there is no black pipe then the closest csst fitting into the home. this was changed in 2012 I believe and they now want the closest black pipe before the closest cast fitting to the panel. no ground rods, no cold water pipes ever. depending on thr juristiction, some want the old way and some want the new. the essence of the new code is that they want to reduce the length of #6 to a minimum
  3. #3
    Join Date
    Feb 2007
    Alexandria, VA
    Posts
    454
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    bonding
    It was my understanding that the CSST can be bonded to any part of the grounding electrode system.
  4. #4
    Join Date
    Dec 2013
    Kansas Cty, Mo, USA
    Posts
    478
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    From what I've seen, there's absolutely no consensus as to the best method....
    Where on the gas line?
    1) Entry point of house, before first fitting
    2) in front of csst, nearest pipe
    3) in front of csst, nearest fitting
    4) on csst nut
    To where?
    1) main panel
    2) ground rod
    3) water line entry point, before first fitting
    4) anywhere on any copper water pipe
    I've seen every combination of the above, from city inspectors. So I don't guess, I ask.
    Last one I did was #1 to #3 plus #3 to #1
  5. #5
    Join Date
    Mar 2008
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    10,526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Greg1707 View Post
    The issue isn't really bonding the CSST. It's the bonding of the incoming gas line to the main panel if CSST is present.
    Cheers and Stay Safe,
    Marky the Sparky