    "do not connect to AFCI protected circuit"

    I was reading the supplied "installation manual" with a 120v Chandelier lift. It states: "do not connect motor to AFCI protected circuit".
    It is to be installed in a "residential dwelling".
    The code's position:
    "210.12 Arc-Fault Circuit-Interrupter Protection. Arcfault
    circuit-interrupter protection shall be provided as required
    in 210.12(A) (B), and (C). The arc-fault circuit interrupter
    shall be installed in a readily accessible location.
    (A) Dwelling Units. All 120-volt, single-phase, 15- and
    20-ampere branch circuits supplying outlets or devices installed
    in dwelling unit kitchens, family rooms, dining
    rooms, living rooms, parlors, libraries, dens, bedrooms,
    sunrooms, recreation rooms, closets, hallways, laundry areas,
    or similar rooms or areas shall be protected by any of
    the means described in 210.12(A)(1) through (6): "

    What a poor boy like me to do?
    My sarcasm is of a level that many of lower intelligence think I am.

  2. #2
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,692
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tadavidson View Post
    I was reading the supplied "installation manual" with a 120v Chandelier lift. It states: "do not connect motor to AFCI protected circuit".
    It is to be installed in a "residential dwelling".
    The code's position:
    "210.12 Arc-Fault Circuit-Interrupter Protection. Arcfault
    circuit-interrupter protection shall be provided as required
    in 210.12(A) (B), and (C). The arc-fault circuit interrupter
    shall be installed in a readily accessible location.
    (A) Dwelling Units. All 120-volt, single-phase, 15- and
    20-ampere branch circuits supplying outlets or devices installed
    in dwelling unit kitchens, family rooms, dining
    rooms, living rooms, parlors, libraries, dens, bedrooms,
    sunrooms, recreation rooms, closets, hallways, laundry areas,
    or similar rooms or areas shall be protected by any of
    the means described in 210.12(A)(1) through (6): "

    What a poor boy like me to do?
    Tell who ever is purchasing the unit that they need to return it and get their money back. I have run into this type of situation with commercial kitchen equipment that included the "do not connect to a GFCI protected circuit" disclaimer, whenever they are told they will not get the sale they usually cave. The problem is the manufacturers to fix, not the code(s).

    Roger
    Moderator

  3. #3
    Join Date
    May 2004
    Posts
    285
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What if I set a 10 amp fused disconnect at the load center and fed this motor's circuit?
    My sarcasm is of a level that many of lower intelligence think I am.

  4. #4
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    60,032
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tadavidson View Post
    What if I set a 10 amp fused disconnect at the load center and fed this motor's circuit?
    I doubt the instructions to the unit allow that either.

  5. #5
    Join Date
    Jun 2015
    Location
    texas
    Posts
    1,698
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by roger View Post
    Tell who ever is purchasing the unit that they need to return it and get their money back. The problem is the manufacturers to fix, not the code(s).

    Roger
    ^^^^^^^
    Seriously this

    To the OP: It's not your responsibility to accommodate equipment that requires code to be violated in order to be installed.

  6. #6
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    18,526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tadavidson View Post
    What if I set a 10 amp fused disconnect at the load center and fed this motor's circuit?
    NEC still requires AFCI protection.

  7. #7
    Join Date
    May 2004
    Posts
    285
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by iwire View Post
    I doubt the instructions to the unit allow that either.
    I know, I know just looking for loop holes.
    My sarcasm is of a level that many of lower intelligence think I am.

  8. #8
    Join Date
    Mar 2003
    Location
    New England
    Posts
    13,932
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If the whole unit is in the attic, I don't see how it needs AFCI protection.

  9. #9
    Join Date
    Mar 2005
    Posts
    226
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by peter d View Post
    If the whole unit is in the attic, I don't see how it needs AFCI protection.
    my thoughts also

  10. #10
    Join Date
    Mar 2003
    Location
    New England
    Posts
    13,932
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I'm assuming you can connect the chandelier to a separate power source?