Does the Code permit me to downsize the neutral on an inverter output circuit? What section? To what size?
Specifically: 11.4 kw inverter @ 240 VAC = 47.5 A @ 125% = 59 Amps ===> 6 AWG wires.
Last time i checked Code requires a neutral on inverter output circuits, so can i use smaller than #6?
Can the EGC be #10 or #8?