    Transformer Neutral required for Inverter Interconnection?

    New to transformers with solar, can you help me out?

    System Specs:
    300 kW of PV with 9 String inverters operating at 480/277 Wye combined with an AC combiner. Combined inverter output power is run through a transformer to step down the combined inverter outputs from 480/277 Wye to a 240 Delta (high leg) and then it will make a supply side connection at the main building service (allowed by AHJ & Utility). The utility service is a 240 Delta High-leg. There are no loads in the inverter combiner, only utility interactive power production sources (solar inverters).

    Question: DO WE NEED TO INSTALL A NEUTRAL CONDUCTOR ON THE 240 DELTA SIDE OF THE TRANSFORMER? (BETWEEN THE TRANSFORMER AND THE UTILITY INTERCONNECTION)

    I have confirmed with the inverter manufacturer that the inverters only use the neutral for instrumentation & voltage referencing (not a current carrying conductor). Note: We will have a neutral installed on the 480/277 side (solar inverter side) of the transformer and this neutral is bonded to ground in the transformer. The inverter manufacturer has stated that this is sufficient for the instrumentation needs of the inverters and the inverters don't need to have a neutral on the 240 Delta side of the transformer.

    The electrical engineer we had review the design is telling us that we need a neutral on the 240 Delta side of the transformer to handle the 120 V (& 208 V High-leg) loads in the building.

    Our master electrician feels that because this is only a utility interactive power production source with a true 240 Delta output from the transformer we don't need the neutral conductor between the transformer and the supply-side connection to the utility. It is purely a power production source that will never run when the utility is down. Therefore we should let any 120 V loads (or high-leg loads) be handled by the utility. Why introduce neutral currents onto our transformer when we don't have to.

    I'm curious to see what you all think. Install the neutral between the transformer and the utility interconnection or leave it out?

  2. #2
    Join Date
    May 2011
    Posts
    5,235
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I'm not an EE, but I'm gonna tell you the answer is No, you do not need a neutral between the service and your transformer.

    My reasoning is as follows...
    1) Believe the inverter manufacturer. They know how their product works. Your EE is obviously less familiar with interactive systems.
    2) The inverters will supply phase-to-phase power to the utility transformer, which will in turn supply current to the neutral on the A-C phase winding, just as it does when powered from the utility side. This is how every single-phase 240V inverter works on a split-phase transformer.
    3) Where would you connect a neutral to a delta transformer?

    Hopefully GoldDigger or another EE will ratify what I'm saying here.

    Caveats:
    1) It would be a good idea to make sure the transformer manufacturer approves of your application just like the inverter manufacturer.
    2) It's tangential to your question, but I've heard that if the service is an open delta, the utility may impose lower limits on how much power you can interconnect.

  3. #3
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,633
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by SunFish View Post
    The electrical engineer we had review the design is telling us that we need a neutral on the 240 Delta side of the transformer to handle the 120 V (& 208 V High-leg) loads in the building.
    The engineer needs to go back to schooll!
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  4. #4
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    21,385
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If the service is 240/120V 3Ø 4W (delta high leg) it is required to bring the neutral circuit conductor to the service disconnecting means. After the service disconnecting means, a neutral circuit conductor is not required to be run if it is not required for normal operation of the circuit, such as the primary of your delta-wye transformer.
    I will have achieved my life's goal if I die with a smile on my face.

  5. #5
    Join Date
    Apr 2006
    Location
    Springfield, MA, USA
    Posts
    3,545
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You have 2 transformers; the utility supply transformer and the solar interconnect transformer.

    The utility supply transformer 240V _secondary_ has a neutral which must be connected to supply your 120V loads.

    The solar interconnect transformer 240V _primary_ is a delta load, and should not have a neutral connection on the primary side.

    If the solar interconnect transformer has a delta primary and a wye secondary, it very likely does not have a neutral tap on the delta side. If it did have a neutral tap, and you connected it, then you would very likely see significant circulating currents between the two transformers.

    -Jon

  6. #6
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    10,961
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by SunFish View Post
    New to transformers with solar, can you help me out?

    System Specs:
    300 kW of PV with 9 String inverters operating at 480/277 Wye combined with an AC combiner. Combined inverter output power is run through a transformer to step down the combined inverter outputs from 480/277 Wye to a 240 Delta (high leg) and then it will make a supply side connection at the main building service (allowed by AHJ & Utility). The utility service is a 240 Delta High-leg. There are no loads in the inverter combiner, only utility interactive power production sources (solar inverters).

    Question: DO WE NEED TO INSTALL A NEUTRAL CONDUCTOR ON THE 240 DELTA SIDE OF THE TRANSFORMER? (BETWEEN THE TRANSFORMER AND THE UTILITY INTERCONNECTION)

    I have confirmed with the inverter manufacturer that the inverters only use the neutral for instrumentation & voltage referencing (not a current carrying conductor). Note: We will have a neutral installed on the 480/277 side (solar inverter side) of the transformer and this neutral is bonded to ground in the transformer. The inverter manufacturer has stated that this is sufficient for the instrumentation needs of the inverters and the inverters don't need to have a neutral on the 240 Delta side of the transformer.

    The electrical engineer we had review the design is telling us that we need a neutral on the 240 Delta side of the transformer to handle the 120 V (& 208 V High-leg) loads in the building.

    Our master electrician feels that because this is only a utility interactive power production source with a true 240 Delta output from the transformer we don't need the neutral conductor between the transformer and the supply-side connection to the utility. It is purely a power production source that will never run when the utility is down. Therefore we should let any 120 V loads (or high-leg loads) be handled by the utility. Why introduce neutral currents onto our transformer when we don't have to.

    I'm curious to see what you all think. Install the neutral between the transformer and the utility interconnection or leave it out?
    Leave it out if you want; I don't think it would carry any current, anyway. The inverters certainly don't need it since you have a separately derived system with a new grounded neutral on the 480/277V side.

    One thing that you should check out, though, if you haven't already: Many high leg services have a much smaller transformer driving the B phase and your system will feed all three phases equally. You need to be sure that you don't overload the transformer driving the high leg.

  7. #7
    Join Date
    Jun 2015
    Location
    Newport County, Rhode Island, USA
    Posts
    655
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by SunFish View Post
    I have confirmed with the inverter manufacturer

    The electrical engineer we had review the design

    Our master electrician feels that because

    Install the neutral between the transformer and the utility interconnection or leave it out?

    a supply side connection at the main building service (allowed by AHJ & Utility)
    You didn't exactly say you've talked to the people that ^^^ make the decision.
    You are connecting to the POCO's xfmr, they do the calcs to make sure everything is ok.
    They have info that the other folks don't, (DG saturation?) and if they allow it, they have guidelines.
    Of course, the guidelines sometimes say "please contact us"...

    Just a reference example, fig. 4 is on pg. 34 ( https://www9.nationalgridus.com/non_...str_esb756.pdf )

    NatGrid ESB 756:

    If the Customer is permitted to interconnect through an un-grounded source,
    a “zero-sequence” voltage scheme will be required on the primary
    side of the approved delta primary wound transformer supplying the DG
    system. In cases where the Company’s EPS is an ungrounded circuit, the
    scheme may be waived at the Company’s discretion on a case by case
    basis. See Figure4 for additional information

    Where the Company provides secondary service, the Company’s transformer is an
    equipment standard for service delivery voltages offered in M.D.P.U. 1192; see
    Section 3 in ESB 750. Non-standard transformers are not provided by the Company.
    The Company will determine when dedicated services and a dedicated transformer
    are required in order to reduce the impact on other adjacent customers. The need
    for a dedicated transformer(s) may be determined at any point in the generator’s life
    cycle.

    Any DG or aggregate DG below 500kW in a Customer’s facility may be permitted to
    utilize a primary delta - secondary wye grounded or primary wye grounded –
    secondary wye grounded transformer with an ungrounded source. The Company
    reserves the right to require an effectively grounded source for generation 250kW-
    500kW depending on DG saturation and other conditions on individual feeders.

  8. #8
    Join Date
    May 2011
    Posts
    5,235
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by PVfarmer View Post
    ...

    NatGrid ESB 756:

    If the Customer is permitted to interconnect through an un-grounded source,
    a “zero-sequence” voltage scheme will be required on the primary
    side of the approved delta primary wound transformer supplying the DG
    [FONT=sans-serif]system. ...
    A high leg delta is not an ungrounded source.

  9. #9
    Join Date
    Jun 2015
    Location
    Newport County, Rhode Island, USA
    Posts
    655
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    A high leg delta is not an ungrounded source.
    There ya go again: telling me something I know quite well, and ignoring my perfectly good advice: talk to the POCO.

    Are you implying any of this could be done *without* talking to the POCO!
    Hmm.

  10. #10
    Join Date
    May 2011
    Posts
    5,235
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by PVfarmer View Post
    There ya go again: telling me something I know quite well, and ignoring my perfectly good advice: talk to the POCO.
    Then you brought up something that you knew was off topic, which I'd ask you not to do again.

    Are you implying any of this could be done *without* talking to the POCO!
    Hmm.
    Talking to the POCO isn't always important, but I did give similar advice as you in the first response in this thread. It's still tangential to the OP's question though.