    480V Delta, 3-phase, 3-wire (ungrounded) service

    A building built in the 60's, has a 480V delta, 3phase, 3wire, ungrounded service and a 120/208V, 3ph, 4wire grounded service.

    Can somebody tell me what year the ground detection sensing equipment became a requirement per NEC 250.21 (B) for the ungrounded delta?

    I understand all the theory behind and why we need this sensing equipment, I just would like to know if it met code when it was constructed back in the 60's.

    The ground electrode system is fine and both services are tied to the same ground electrode system, the 120/208V service is fine too.
    Thanks for your help.

  2. #2
    Join Date
    Dec 2010
    Posts
    1,497
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    2005
    Attached Images Attached Images  
    The more they overthink the plumbing, the easier it is to stop up the drain

  3. #3
    Join Date
    Mar 2007
    Location
    Las Vegas, NV
    Posts
    67
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thank you, I appreciate your help dkidd !!!