    Paddle Fan Switch Location Rules?

    The contractor that is building my home is arguing with me about the location of the paddle fan switch. This fan is one you would typically see in a bathroom. You would think they would have put the switch inside the bathroom, but they put it in the living room. Granted, all you have to do is stick your hand outside the bathroom to turn the fan on. Bathroom is adjacent to the living room. It's just stupid. The switch for the bathroom light is in the bathroom. My guess is they wired it to the wrong switch accidentally and didn't notice.

    I was wondering if there was something in the code that would state a requirement to have the paddle fan switch located in the same room the fan is in.

    P.S. I purchased the house on inventory, it isn't a custom build home. I don't really have a leg to stand on unless I can prove it doesn't meet code.



  2. #2
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    8,158
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    There are essentially no requirements on where the light switch goes, exception for stairway lighting. A light switch does not have to be in the same room, and can be 7 feet from the floor.
    There is a restriction on paddle fans in bathrooms, they can't be above a tub or shower.
    Its common still to see the bathroom light switch outside the bathroom.
    Moderator-Washington State
    Ancora Imparo

  3. #3
    Join Date
    Jul 2007
    Location
    Clark County, NV
    Posts
    2,147
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Agreed. Very odd (I'd consider it poor workmanship) to have the fan and light switched from opposite ends of the wall, but no prohibition on it that I can recall.

  4. #4
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tom baker View Post
    There are essentially no requirements on where the light switch goes, exception for stairway lighting.
    210.70(A)(3)
    "Electricity is really just organized lightning." George Carlin


    Derek

  5. #5
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    2,007
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by TeslaEE View Post
    ..I don't really have a leg to stand on unless I can prove it doesn't meet code.
    Unless Texas energy code requires a vacancy switch in bathrooms, like CA Title-24 energy codes, paying for the change order may be unavoidable.
    Roger Ramjet NoFixNoPay

  6. #6
    Join Date
    Dec 2015
    Location
    Texas
    Posts
    196
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Texas does not require Vacancy/Occupancy sensors for Residential single dwelling.

    Edit: Depending on where you're located though, Texas has adopted the 2017 NEC.

    Under the 2017 NEC 422.31 (Disconnection of Permanently Connected Appliances):

    (A): Rated at Not over 300 VA or 1/8 HP: For permanently connected appliances rated at not over 300VA or 1/8HP, the branch circuit overcurrent device shall be permitted to serve as the disconnecting means where the switch or circuit breaker is within sight from the appliance or is lockable in accordance with 110.25.

    The bold section is new, and if you agree that a paddle-fan is an appliance, and you cannot see the switch as it's on the other side of the wall, you may have a leg to stand on.
    Last edited by tw1156; 10-31-17 at 03:52 PM.

  7. #7
    Join Date
    Feb 2016
    Location
    Illinois
    Posts
    1,400
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If I recall correctly, in some countries the bathroom light switch(es) must be located outside the bathroom.
    Not really helpful to the OP, but perhaps an interesting anecdote.

  8. #8
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,298
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by TeslaEE View Post
    The contractor that is building my home is arguing with me about the location of the paddle fan switch. This fan is one you would typically see in a bathroom. You would think they would have put the switch inside the bathroom, but they put it in the living room. Granted, all you have to do is stick your hand outside the bathroom to turn the fan on. Bathroom is adjacent to the living room. It's just stupid. The switch for the bathroom light is in the bathroom. My guess is they wired it to the wrong switch accidentally and didn't notice.

    I was wondering if there was something in the code that would state a requirement to have the paddle fan switch located in the same room the fan is in.

    P.S. I purchased the house on inventory, it isn't a custom build home. I don't really have a leg to stand on unless I can prove it doesn't meet code.


    You typically don't see a paddle fan in the bathroom but do see exhaust fan. Regardless what you have, you do have a leg to stand on, don't pay him. Even though it is not NEC violation to have the switch outside but it is a violation of common sense.
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  9. #9
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,298
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ramsy View Post
    Unless Texas energy code requires a vacancy switch in bathrooms, like CA Title-24 energy codes, paying for the change order may be unavoidable.
    CA vacancy sensor applies to bathroom incandescent fixtures only, am I not correct?
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  10. #10
    Join Date
    Jul 2005
    Location
    LA basin, CA
    Posts
    2,007
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by edward View Post
    CA vacancy sensor applies to bathroom incandescent fixtures only, am I not correct?
    You can see for yourself, at least one bath light switch shall be controlled by an occupancy sensor.
    "2016 Building Energy Efficiency Standard"

    New construction is not part of my service business, but replacements are, and making sense of the new JA8 light bulb is tricky with California's "2016 Building Energy Efficiency Standard"

    How are we to re-lamp when JA8 is not marked on any bulb, packaging, and apparently not sold in any stores?
    Roger Ramjet NoFixNoPay