Hi All,low voltage cable can occupy the same J box as long as the insulation is rated for the highest voltage in the box.
Geo
Geo
Depends on what you are calling low voltage cable. It is not absolutely true when we get into both power wiring and Article 725 applications, for example.Hi All,low voltage cable can occupy the same J box as long as the insulation is rated for the highest voltage in the box.
Geo
While 300.3(C) may lead you to think that, you also have to look to the Informational Notes that follow that section.Hi All,low voltage cable can occupy the same J box as long as the insulation is rated for the highest voltage in the box.
Geo
Permitted or otherwise, I wouldn't put signal cables in the same J box as power cables.Hi All,low voltage cable can occupy the same J box as long as the insulation is rated for the highest voltage in the box.
Geo
Permitted or otherwise, I wouldn't put signal cables in the same J box as power cables.
Yes, data.Signal as in data? No I would not either
Low voltage as in 24volts from the secondary side of a transformer for LV landscape lighting,