Thread: Relocating SEC's from meter lugs to new main panel: materials and neutral splice:Calf

  1. #1
    Join Date
    Jul 2017
    Location
    Berkeley California USA
    Posts
    73
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Relocating SEC's from meter lugs to new main panel: materials and neutral splice:Calf

    Hey all,

    I have two little questions:

    1) Does anyone know off hand if pg&e prohibits PVC from meter socket to new main panel/disconnect? Greenbook says no plastic at weatherhead/periscope.

    2) Also, does anyone know if the neutral can be spliced / retapped in the meter can? If I'm lucky it will reach to the new panel but I need to be prepared to run new wire from meter can for both phases and the neutral.

    Is this clear?

    Thx!

    Humble_hank

  2. #2
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    1. Hopefully PG&E allows PVC between meter can and first disconnecting means, best method IMO. No parallel neutral current path that a metallic nipple creates.

    2. I do not really understand what you mean. Why are trying to splice in a meter base? Retapped???

    FWIW, POCOs generally disallow anything out of the norm in a meter.
    "Electricity is really just organized lightning." George Carlin


    Derek

  3. #3
    Join Date
    Jul 2017
    Location
    Berkeley California USA
    Posts
    73
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    reply: meter run q's

    i had originally thought i would leave existing
    meter and simply replace current disconnect which is quite a sketchy item;
    in a cubby under meter. It occured
    though to me that while the two phase wires might be long enough , there was a chance that if they were not i might have to replace them from meter lugs. By that thinking I realized that if they were too short, likely neutral would be as well. I was seeking to avoid repulling new neutral from weather head in that scenario, hence could i splice new neutral in meter can.

    However,
    I'm leaning now towards doing new meter and main disconnect
    combination. It
    will be a lot easier. Going to site today to measure then to parts store.

    Thx!


    Quote Originally Posted by jumper View Post
    1. Hopefully PG&E allows PVC between meter can and first disconnecting means, best method IMO. No parallel neutral current path that a metallic nipple creates.

    2. I do not really understand what you mean. Why are trying to splice in a meter base? Retapped???

    FWIW, POCOs generally disallow anything out of the norm in a meter.
    Last edited by docj67; 02-16-18 at 01:12 PM. Reason: typo

  4. #4
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,630
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I can't speak for PG&E policy but the meter sockets in use in our areas are designed to accept "line and load" neutral termination on the built-in lug,.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  5. #5
    Join Date
    Jul 2017
    Location
    Berkeley California USA
    Posts
    73
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    thx: only seen one meter socket so far...

    and neutral was fed from quad tap. was 4 plex building in other post on grounding.

    service equipment was gutter w 4 meters and 4 disconnects. each meter had neutral fed behind lugs down into nipple to disconnect w two phases from lugs.

    i'm new.
    sometimes i wonder how i got here.

    js

  6. #6
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by docj67 View Post

    sometimes i wonder how i got here.

    js
    Enter>>>>>Insert smart aleck crack about Berserkley>>>>>>>Exit.
    "Electricity is really just organized lightning." George Carlin


    Derek

  7. #7
    Join Date
    Jul 2017
    Location
    Berkeley California USA
    Posts
    73
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    Enter>>>>>Insert smart aleck crack about Berserkley>>>>>>>Exit.
    bring it bro!

    come on let's hear it!

  8. #8
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by docj67 View Post
    bring it bro!

    come on let's hear it!
    Easy, I joke about all the Bay Area. Grew up here, been saying Berserkley since I was a kid.

    Sitting in SF now, ATT Park, staring at Alemeda.
    "Electricity is really just organized lightning." George Carlin


    Derek

  9. #9
    Join Date
    Jul 2017
    Location
    Berkeley California USA
    Posts
    73
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    aww i was hopin' you'd talk some funny ...t

    don't
    misread my tone i
    love hard humor

    Dave Chappelle?

    Quote Originally Posted by jumper View Post
    Easy, I joke about all the Bay Area. Grew up here, been saying Berserkley since I was a kid.

    Sitting in SF now, ATT Park, staring at Alemeda.

  10. #10
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by docj67 View Post
    aww i was hopin' you'd talk some funny ...t

    don't
    misread my tone
    love hard humor

    Dave Chappelle?
    Hard humor will get one’s post deleted here.

    Dry British or American slapstick is more my thing.
    "Electricity is really just organized lightning." George Carlin


    Derek

Tags for this Thread