    Running NM cable between door head jamb and top header?

    I'm looking at a really easy run for some NM cable, but it is between the head jamb of a door and the top header. All other paths are much harder. Thickest part of the jam is over 1 1/4 inches and there's another inch of air space before the top header.

    It seems to meet the NEC requirements for NM cable, but somehow it makes me uncomfortable. Is running nm cable here OK? If it were to be protected, how?
    There are plastic boxes on either side of the run, which makes armored cable a bit more awkward.

    Name:  door jamb nm electrical wiring.jpg
Views: 376
Size:  84.6 KB

  2. #2
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    So long as the cable isn't running through space where the door opens, you are fine.
    Electricians do it until it Hertz!

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,315
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Not an issue if you 1.25" back from the edge as required. Even AC cable will be no match for the carpenters nail gun.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted