NEC 201.5(2)(a)

Status
Not open for further replies.

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
I'm not going to quote it all here, but this section seems to me to say that we now (as of NEC2014) need to use red, red striped, or continuously "+" notated wires for our #10 home runs - no taping. Whaddya think?
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
I'm not going to quote it all here, but this section seems to me to say that we now (as of NEC2014) need to use red, red striped, or continuously "+" notated wires for our #10 home runs - no taping. Whaddya think?
I think you mean 210.5(C)(2) (2014).

As to question, I think the PV DC conductors from a PV panel to an inverter are not branch circuit conductors. See the definition of branch circuit in Article 100.

Cheers, Wayne
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I'm not going to quote it all here, but this section seems to me to say that we now (as of NEC2014) need to use red, red striped, or continuously "+" notated wires for our #10 home runs - no taping. Whaddya think?

there is no article 201 in my copy of the 2014 NEC.
 