Thread: CSST bonding to sub panel

  1. #11
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,486
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    good point, in that respect the nec is being very accomodating of other trades ~RJ~

  2. #12
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,321
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    good point, in that respect the nec is being very accomodating of other trades ~RJ~
    I don't know what CSST instructions say but many seem to think it must go to the electric panel and not to the ISBT though.
    I live for today, I'm just a day behind.

  3. #13
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,440
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    I don't know what CSST instructions say but many seem to think it must go to the electric panel and not to the ISBT though.
    Of the few I have installed, most got split-bolted to the GEC in the crawl space.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  4. #14
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,321
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Of the few I have installed, most got split-bolted to the GEC in the crawl space.
    What few? CSST bonding or the ISBT?
    I live for today, I'm just a day behind.

  5. #15
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    25,440
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    What few? CSST bonding or the ISBT?
    CSST bonding; I don't know what ISBT is.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  6. #16
    Join Date
    Jul 2004
    Location
    Louisville, Kentucky
    Posts
    2,156
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    CSST bonding; I don't know what ISBT is.
    I think it's short for:

    Intersystem Bonding Terminal
    Norb

  7. #17
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,731
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    We have talked about this csst going to the intersystem bonding but at the big meetings it was stated that the intersystem bonding unit was not listed for bonding of csst. Local inspectors still allow it at times however most units have only 3 ports for other utilities so if you use one for the intersystem then you only have 2 left. Can one argue that the csst is another system???

    Consist of a set of terminals with the capacity for connection
    of not less than three intersystem bonding conductors
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  8. #18
    Join Date
    Feb 2018
    Location
    Iowa
    Posts
    302
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kec View Post
    Can someone tell where it states that the #6 bonding wire has to be connected to the main panel and not a sub panel ground bar?

    Here.
    https://cdn-web.iccsafe.org/wp-conte...Notes_CSST.pdf

    "The permanent bonding of corrugated stainless steel tubing (CSST) piping system directly to the grounding electrode system of the structure in which the CSST is installed will lower the voltage build-up on the CSST caused by unintentional energizing from outside sources such as power surges and lightning strikes"


    Must connect to the GEC not to the EGC. Minimum wire size #6 cu.

  9. #19
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,731
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Is there anywhere in the gas code that states the connection must be continuous? I don't think so so if the equipment grounding conductor to the sub panel is a #6 then the csst bonding should be allowed to connect to that panel.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  10. #20
    Join Date
    Feb 2018
    Location
    Iowa
    Posts
    302
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    Is there anywhere in the gas code that states the connection must be continuous? I don't think so so if the equipment grounding conductor to the sub panel is a #6 then the csst bonding should be allowed to connect to that panel.
    It says connect to the grounding electrode system.