User Tag List
Page 1 of 2 1 2 LastLast
Results 1 to 10 of 16
Thread: Watts Calculation Method for 240V Circuits
  1. #1
    Join Date
    Apr 2017
    Florida
    Posts
    63
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I need assistance with determining my Watts correctly with Ohm's law using the amperage reading from my Fluke clamp meter. I welcome anyone who can correct the errors of my ways and offer a brief explanation so I can learn correctly.
    Amperage Readings
    L1: 17.1 Amps
    L2: 17.0 Amps
    Ohms Law
    P(w) = V x I
    Method 1: Calculated ohms law for each leg of the circuit, calculated them individually, then added the wattage together.
    L1: 17.1A x 120V = 2,052 Watts
    L2: 17.0A x 120V = 2,040 Watts
    Total Watts1: 4,092 Watts
    Method 2: Combined amperage for both legs and used 240V by combined average to calculate watts which is double Method 1.
    L1: 17.1 Amps
    L2: 17.0 Amps
    Lt = 34.1 Amps x 240V = 8,184 Watts
    Total Watts2: 8,184 Watts
    Any help with this would be greatly appreciated.
  2. #2
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    20,231
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Cybatrex View Post
    Amperage Readings
    L1: 17.1 Amps
    L2: 17.0 Amps
    Ohms Law
    P(w) = V x I
    L1: 17.1 Amps
    L2: 17.0 Amps
    The problem with your second method is that the same current (approximately) is flowing through the same series circuit between L1 and L2. You only count that current once! That is where your extra factor of two came from.
  3. #3
    Join Date
    Apr 2017
    Florida
    Posts
    63
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    Thank you so much. To clarify,
    I would take the amperage to either L1 or L2 and then multiply by 120V or 240V?
    L1 X 240V = CORRECT 1?
    (L1+L2) X 120V = CORRECT 2?
    What you see in yourself is what you see in the world.
  4. #4
    Join Date
    Dec 2012
    Posts
    20,231
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    1. Yes.
    2. Yes.
    For 240 you can use one L current value if the two are identical
    If they are not identical, you can take the average and multiply it by 240. Algebraically this is 100% identical to the formula in 2.
  5. #5
    Join Date
    Apr 2008
    Ann Arbor, Michigan
    Posts
    7,730
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    180526-0821 EDT
    Cybatrex:
    Change the word watts to volt-amperes. It may be watts, but only if the load is pure resistance like an incandescent bulb, or resistive heater,
  6. #6
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    10,958
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    A common rookie mistake is to think that a 240V 100A 2 pole breaker delivers 200A @240V. 100A on L1 + 100A on L2.
  7. #7
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Amperage Readings
    L1: 17.1 Amps
    L2: 17.0 Amps
    Ohms Law
    P(w) = V x I
    L1: 17.1 Amps
    L2: 17.0 Amps
    If it is 120-0-120V then I suppose L1*120 + L2*120 would be the more accurate. But the 0.1A would be in the neutral but probably not significant. If is is actually there.
  8. #8
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Besoeker View Post
    that is more accurate
    in this case the currents happened to be balanced
    not always (or even usually) the case
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,086
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Amperage Readings
    L1: 17.1 Amps
    L2: 17.0 Amps
    Ohms Law
    P(w) = V x I
    L1: 17.1 Amps
    L2: 17.0 Amps
    If you only have a two wire circuit you can't have a different current on one conductor then you have on the other, there is only one current path and current is same everywhere in the circuit. I'm sure accuracy of the measuring method is what resulted in the minor difference you did measure. That said and as others have been pointing out - you have ~17 amps at 240 volts and not ~17 amps at 120 volts - times two.
    Add a third point in the system it gets more complicated, especially if you have 208/120 system. That situation you could possibly have 17 amps at 120 volts - times two, or even three. But that never can happen when there is only a two wire circuit.
    I live for today, I'm just a day behind.
  10. #10
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Ingenieur View Post
    Yes. And Gar's point about it being VA rather than W should be noted.
    A point in passing. I usually use the letter or symbol for the unit - W rather that Watts.
    This stems from losing a mark on an exam question for spelling out the unit in the answer.
    I was told that spelling it out was the incorrect thing to do. IDK whether that's true or not. But it stuck with me.
    Mods, forgive the digression.
Tags for this Thread
Posting Permissions
  • You may not post replies
  • You may not edit your posts