    Been putting together a voltage drop calculation spreadsheet based on the NEC tables and noticed something surprising. I though that the voltage drop in a circuit would always increase with decreasing power factor. That tends to be the case with larger wire sizes (3/0 and above) but is definitely not the case with smaller wires. These calculations were based on Chapter 9 Table 9, I could show my work if you want but taking the following parameters, the voltage drop is worst with unity pF:
    A=50A
    wire size=8awg
    length=50
    voltage=120
    phase=1
    Here are the percent voltage drops I got starting with pf=1, then .9, .8, .7, .6 ,......,.2
    pf=1 - 3.24%
    3.04%
    2.76%
    2.47%
    2.17%
    1.86%
    1.55%
    1.23%
    pf=0.2 - 0.92%
    This happens for all the wires up to 2/0. What gives? Is it just due to the impedances of smaller wires?
  2. #2
    Join Date
    Jul 2005
    LA basin, CA
    Posts
    2,007
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shespuzzling View Post
    ..I though that the voltage drop in a circuit would always increase with decreasing power factor..
    My Tbl-9 calculator followed your results also - for purely resistive loads only. Very interesting, perhaps the engineers can explain this?
    However, for inductive-motor loads adjusted per NEC 220.18(A), both Current and Voltage Drop increase with decreasing Power Factor, inversely proportional, as expected.
    Roger Ramjet NoFixNoPay
  3. #3
    Join Date
    Oct 2012
    new york
    Posts
    48
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    any thoughts?
  4. #4
    Join Date
    Jul 2005
    LA basin, CA
    Posts
    2,007
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Ask Ingenieur to join this discussion.