    Number of Splicing allowed by NEC

    As per NEC article 110.10(B) , splicing of cable is allowed. however , i cannot find a reference for maximum or minimum splices allowed by NEC . I have a cable 3C x 240 MM2 to be spliced twice ( total length is 800 meter ) . is it acceptable to NEC to splice low voltage cable underground more than one splice . I am using identified splice kit for LV and underground .

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,505
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I know of no NEC limit on the number of splices in a run.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,907
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    An 800 meter run at LV eh? What size and load are we talking about out of curiosity?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  4. #4
    Join Date
    Mar 2003
    Location
    New York
    Posts
    1,940
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    What cable is that?
    What is low voltage 4160v, 120volt , 12v?
    Your in Saudi do they follow NEC or are you on base?
    Question answer is splice away, but is better to do non splice when possible.

  5. #5
    Join Date
    Nov 2017
    Location
    KSA
    Posts
    6
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    For information ,

    Cable should be spliced due to standard size reels with full length cables of manufacturer ( 350 meter ) .

    Cable Description : Power cable , 3 Conductors, 240 MM2 ( 500kmcil) , 600/1000V , XLPE/SWA/PVC .
    Low Voltage : 480V
    MAX LOAD : 29.6 KVA
    Nb. Phases : three .

    To Mr. Sameguy , NEC and IEC standards are applicable in Saudi Arabia .


    Thanks for everyone's reply .

  6. #6
    Join Date
    Sep 2004
    Location
    Vancouver, WA
    Posts
    747
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    How many is too many

    A typical electrical installation has 100's of splices/connections in series and we do this every day. Every time we terminate a wire, we add a "splice." Think of a daisy-chain of receptacles: the hot leg has two splices, the neutral has two, so each receptacle adds 4 splices to the current path. So, with 10 receptacles on a circuit, there are 40 "splices" in the current path. Add the breaker and neutral terminals at the panel, the main breaker connections, the service wire connections. Sometimes it is amazing that it even works!
    e^(i pi) = -1

  7. #7
    Join Date
    Mar 2003
    Location
    New York
    Posts
    1,940
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Khaledhn View Post
    For information ,

    Cable should be spliced due to standard size reels with full length cables of manufacturer ( 350 meter ) .

    Cable Description : Power cable , 3 Conductors, 240 MM2 ( 500kmcil) , 600/1000V , XLPE/SWA/PVC .
    Low Voltage : 480V
    MAX LOAD : 29.6 KVA
    Nb. Phases : three .

    To Mr. Sameguy , NEC and IEC standards are applicable in Saudi Arabia .


    Thanks for everyone's reply .
    Thank you.