Thread: May I ask a question about the single vs two phase stuff

  1. #1141
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,285
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sahib View Post
    So the only 240/120V with or without neutral is incapable of producing a rotating magnetic field by itself and so must be a single phase system.
    That's always been my take.

    Two lines from a wye supply with the neutral can supply two transformers and create an open delta, but two lines alone are definitely a single-phase source.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  2. #1142
    Join Date
    Sep 2008
    Location
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    That's always been my take.

    Two lines from a wye supply with the neutral can supply two transformers and create an open delta, but two lines alone are definitely a single-phase source.
    The 120-0-120 arrangement is two lines phase displaced by 180° plus a neutral.
    I think we can all agree on that.
    Si hoc legere scis nimium eruditionis habes.

  3. #1143
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,957
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Besoeker View Post
    The 120-0-120 arrangement is two lines phase displaced by 180° plus a neutral.
    I think we can all agree on that.
    Actually, I am afraid we can't.
    Some say that 120-0-120 has two line to neutral voltages, of which one is the negative of the other. Others say that it has two line to neutral voltages offset in phase by 180 degrees. The two are equivalent for pure sine waves and ones with symmetry about the 90 degree time point. But if the basic waveform is sufficiently far from ideal (a sawtooth wave is a good example to look at) the two descriptions (negative versus 180 degree phase shift) are not identical.












    [/B] equivalent.

  4. #1144
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,285
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Besoeker View Post
    The 120-0-120 arrangement is two lines phase displaced by 180° plus a neutral.
    I think we can all agree on that.
    I agree that we can't. The only application of 180 degrees is to refer to instantaneous polarity, and that's only because of the choice to use the center tap as a stationary reference point. There is no displacement.

    Added: If viewed on a dual-channel o-scope, the two waves might appear displaced in time, but the fact is they rise and fall in sync in opposite directions from zero simultaneously; thus, it's a matter of polarity.


    You really need to find and read that incredibly long thread we did.
    Last edited by LarryFine; 01-11-19 at 06:53 AM.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  5. #1145
    Join Date
    Sep 2008
    Location
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    Actually, I am afraid we can't.
    Some say that 120-0-120 has two line to neutral voltages, of which one is the negative of the other. Others say that it has two line to neutral voltages offset in phase by 180 degrees. The two are equivalent for pure sine waves and ones with symmetry about the 90 degree time point. But if the basic waveform is sufficiently far from ideal (a sawtooth wave is a good example to look at) the two descriptions (negative versus 180 degree phase shift) are not identical.
    [/B] equivalent.
    Yes. Two. Displaced in phase.
    i.e. not the same phase.
    Si hoc legere scis nimium eruditionis habes.

  6. #1146
    Join Date
    May 2011
    Posts
    4,874
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Besoeker View Post
    The 120-0-120 arrangement is two lines phase displaced by 180° plus a neutral.
    I think we can all agree on that.
    I wonder if you will get anyone to agree with that.

    The two hot legs brought by themselves without the neutral have a voltage which isn't displaced from anything.

  7. #1147
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    10,461
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Besoeker View Post
    The 120-0-120 arrangement is two lines phase displaced by 180° plus a neutral.
    I think we can all agree on that.
    You're new around here, aren't ya'?

    (I know you aren't)

  8. #1148
    Join Date
    May 2011
    Posts
    4,874
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sahib View Post
    So the only 240/120V with or without neutral is incapable of producing a rotating magnetic field by itself and so must be a single phase system.
    Quote Originally Posted by mivey View Post
    ...

    Think about it: The 3-wire quadrature two-phase we get from a transformer bank is just the 120/208 system shifted from 120d to 90d. We could also call 120/208 two-phase except that the name has already been taken by the quadrature two-phase system.
    Here we are (finally?) getting back to what the OP was actually asking about. How can 120/240 be considered more than one phase if it is incapable of producing a rotational field? If that's what single phase means (no rotational field) then 120/240 is single phase. But I doubt that we can get Boeseker to agree that that's the meaning.

    To that point, Mivey, you're exactly correct that the three wire quadrature two-phase is qualitatively similar to the 120/208 3-wire system. But I don't agree that the latter is not called 'two-phase' because the name is already taken. After, all, a lot of utilities call it 'single phase' and that name was already taken, too. Which just proves that people have been using disparate conventions for too long, and this will never get resolved. At least not in a free society. I concede the point on that.

  9. #1149
    Join Date
    Sep 2008
    Location
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    I wonder if you will get anyone to agree with that.

    The two hot legs brought by themselves without the neutral have a voltage which isn't displaced from anything.
    But that wouldn't be 120-0-120, would it..................
    Si hoc legere scis nimium eruditionis habes.

  10. #1150
    Join Date
    Sep 2008
    Location
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    Here we are (finally?) getting back to what the OP was actually asking about. How can 120/240 be considered more than one phase if it is incapable of producing a rotational field? If that's what single phase means (no rotational field) then 120/240 is single phase. But I doubt that we can get Boeseker to agree that that's the meaning.
    With respect, the capability of producing a rotational field is not of relevance. I designed multi-phase high current rectifiers. No rotation involved.
    Si hoc legere scis nimium eruditionis habes.