User Tag List
Page 2 of 126 FirstFirst 1 2 3 4 12 52 102 ... LastLast
Results 11 to 20 of 1259
Thread: May I ask a question about the single vs two phase stuff
  1. #11
    Join Date
    Jan 2011
    United States
    Posts
    8,805
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by Russs57 View Post
    But from a pratical point....I could have two motors, both called single phase, feed from a 3 phase 480/277 supply. Both would have run caps, but one would get 277 and one would get 480. Seems the one that is 480 is a true two phase motor (albeit 120 degrees apart) and therefore should be able to run without the cap.....but it doesn't seem to.
    I feel I'm failing to understand something here.
    Its only 2 wires- you would need to make use of the neutral. 3 wires to the motor and 2 windings.
    I'm in over my head...
  2. #12
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    the 480 is not 2 ph (although comprised of 2 phase lines)
    Vab is a ph
    Vbc
    Vca
    each is a single ph (the sum of 2 phase coils in a wye)
  3. #13
    Join Date
    Apr 2007
    Berkeley, CA
    Posts
    1,803
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The two legs for the 480 volt motor are only 120 degrees apart relative to the neutral. For a circuit with only two wires, there is no notion of phase. When discussing phases, there are necessarily at least 3 wires involved: one defines a common reference, so that the phase difference between the other two wires can be described.
    Cheers, Wayne
  4. #14
    Join Date
    Nov 2014
    Miami, Florida, USA
    Posts
    208
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Thank you gentlemen.
  5. #15
    Join Date
    Apr 2008
    Ann Arbor, Michigan
    Posts
    7,620
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    180722-1321 EDT
    I have two single phase generators driven by one motor with a 1 to 1 ratio between the motor and each generator. Additionally there is an adjustable mechanical coupling between the two generators such the relationship mechanically can be anywhere between and including 0 and 360 degrees. Is this system a two phase source?
    By design this system has two generators that are synchronized.
  6. #16
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    They are "out of phase" from one another from their relationship to a particular reference point at any given moment in time.
    Isn't that all moments in time? They are out of phase all the time. That's not nit picking - I think it's an important concept to understand.
    There is no "phase" relationship that creates a rotating field for an ac induction type motor without additional methods being used to create such rotating field on such "split phase" source.
    True. But does that doesn't mean that you don't have two phases displaced by 180° from each other.
  7. #17
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,165
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It is two phases in relation to the entire three phase supply, but to the motor being supplied you only have a single voltage and a single current wave form in the supply conductors, and the "phase angle" between two points is always 180 degrees. As already mentioned that 120 degree angle is when referenced to the neutral point of the overall supply system.
    Comes down to what I earlier mentioned exact meaning of "phase" depends on what is being referenced to what and that the word phase alone is too generic to mean the same thing for all conditions we use this word for.
    I live for today, I'm just a day behind.
  8. #18
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by gar View Post
    180722-1321 EDT
    yes
    and if set at 180 deg and 1 leg from each commoned indistinguishable from 120/240/1 split phase
  9. #19
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jaggedben View Post
    An important reason not to call split-phase 'two-phase' is that two-phase actually means something else.
    Otherwise, mathematically sin(n)=-sin(n+180), and thus it's a bit pointless to argue over which is a 'better' mathematical representation of what you read with your meter. Just specify which probe on your scope is being used as reference.
    From a conceptual point of view, if the two sources are actually derived from the same transformer primary, it makes more sense to think of it as 'single phase with a center tap'. If they are something else (say two inverters that can use software to have various relationships) then perhaps speaking about mutliple phases is more justified. Ultimately, however, one's obligation is only to employ words to accurately represent what is being done physically, which can be done multiple ways as long as one defines terms clearly. Trying to settle what it 'is' is relatively pointless.
    "Electricity is really just organized lightning." George Carlin
    Derek
  10. #20
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
Posting Permissions