Thread: Hot tub disconnect inside 5’ from water

  1. #1
    Join Date
    Mar 2018
    Location
    PA
    Posts
    62
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Hot tub disconnect inside 5’ from water

    Hi guys, we are installing power for a hot tub that the people put in a bump in, in the back of house. How the house was built, the hot tub will fit perfectly in the nook. There is only about 20-24” of space from the 3 sides of hot tub and the house. Looking at where to install the disconnect, it looks like it will have to go on the front of the nook so the disconnect will not technically be “within line of sight” of the hot tub. I don’t think we have the space to install the disconnect in back of hot tub and build a separating structure between the two. Any suggestions ????

  2. #2
    Join Date
    May 2014
    Location
    AZ
    Posts
    2,563
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dansos View Post
    Hi guys, we are installing power for a hot tub that the people put in a bump in, in the back of house. How the house was built, the hot tub will fit perfectly in the nook. There is only about 20-24” of space from the 3 sides of hot tub and the house. Looking at where to install the disconnect, it looks like it will have to go on the front of the nook so the disconnect will not technically be “within line of sight” of the hot tub. I don’t think we have the space to install the disconnect in back of hot tub and build a separating structure between the two. Any suggestions ????
    What type of hot tub is it? A stand-alone manufactured UL listed spa?

  3. #3
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,363
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dansos View Post
    Hi guys, we are installing power for a hot tub that the people put in a bump in, in the back of house. How the house was built, the hot tub will fit perfectly in the nook. There is only about 20-24” of space from the 3 sides of hot tub and the house. Looking at where to install the disconnect, it looks like it will have to go on the front of the nook so the disconnect will not technically be “within line of sight” of the hot tub. I don’t think we have the space to install the disconnect in back of hot tub and build a separating structure between the two. Any suggestions ????
    Ask if going up is acceptable

    a means of discconet can be 3 metres now (6'8")

    measure both horz & vert to the tub rim

    ~RJ~

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,075
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    Ask if going up is acceptable

    a means of discconet can be 3 metres now (6'8")

    measure both horz & vert to the tub rim

    ~RJ~
    Did you mean 2 meters?
    I live for today, I'm just a day behind.

  5. #5
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,363
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    yes, thx kwired, guess that reveals how metric I am ~RJ~

  6. #6
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    2,337
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    Ask if going up is acceptable

    a means of discconet can be 3 metres now (6'8")

    measure both horz & vert to the tub rim

    ~RJ~

    There doesn't appear to be a verical component in the measurement. Code says 5ft horizontally.


    NEC 2017 680.13 Maintenance Disconnecting Means. One or more
    means to simultaneously disconnect all ungrounded conductors
    shall be provided for all utilization equipment other than
    lighting. Each means shall be readily accessible and within sight
    from its equipment and shall be located at least 1.5 m (5 ft)
    horizontally from the inside walls of a pool, spa, fountain, or
    hot tub unless separated from the open water by a permanently
    installed barrier that provides a 1.5 m (5 ft) reach path or
    greater. This horizontal distance shall be measured from the
    water's edge along the shortest path required to reach the
    disconnect.

  7. #7
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    2,337
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dansos View Post
    Hi guys, we are installing power for a hot tub that the people put in a bump in, in the back of house. How the house was built, the hot tub will fit perfectly in the nook. There is only about 20-24” of space from the 3 sides of hot tub and the house. Looking at where to install the disconnect, it looks like it will have to go on the front of the nook so the disconnect will not technically be “within line of sight” of the hot tub. I don’t think we have the space to install the disconnect in back of hot tub and build a separating structure between the two. Any suggestions ????
    If the nook looks out to a lawn or other open area you could set the disco on a 4x4 pressure treated post five or more feet away. The disco would not have to be mounted very high as long as the area does not flood.

  8. #8
    Join Date
    May 2014
    Location
    AZ
    Posts
    2,563
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Coppersmith View Post
    If the nook looks out to a lawn or other open area you could set the disco on a 4x4 pressure treated post five or more feet away. The disco would not have to be mounted very high as long as the area does not flood.
    680 is dizzying. I thought residential manufactured UL listed tubs can use OCPD as the disco?

  9. #9
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,075
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by FionaZuppa View Post
    680 is dizzying. I thought residential manufactured UL listed tubs can use OCPD as the disco?
    680.40 says installations must comply with part I and part IV. Back in part I 680.12 addresses maintenance disconnecting means, and says it must be within sight of the equipment.
    I live for today, I'm just a day behind.

  10. #10
    Join Date
    May 2014
    Location
    AZ
    Posts
    2,563
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    680.40 says installations must comply with part I and part IV. Back in part I 680.12 addresses maintenance disconnecting means, and says it must be within sight of the equipment.
    680.12 is rooms & pits. 680.13 in 2017 NEC.
    I was perhaps thinking of the emergency shutoff switch, which is not required for the residential hot tub / spa.

    I use lever style disco, and it's close and visible to the spa, it serves as both disco and emergency shutoff.