    Quote Originally Posted by Dale001289 View Post
    I believe most AHJs would disagree with you. Besides most housekeeping pads are nowhere near 6”


    Sent from my iPhone using Tapatalk
    In 40 years it has never been even a discussion with an inspector on any job that I have seen.
    This is a non issue in New England.

    The OP mentioned a 20” extension. That is too much and should be a violation.
    It should be 3’ to 4’ depending on the condition, or 6”.
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices

  2. #22
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tkb View Post
    In 40 years it has never been even a discussion with an inspector on any job that I have seen.
    This is a non issue in New England.

    The OP mentioned a 20” extension. That is too much and should be a violation.
    It should be 3’ to 4’ depending on the condition, or 6”.
    It’s a judgement call.
    I’ve seen it go both ways - depends on QA/QC inspectors. In Petro-chem facilites they tend to be less tolerant.


    Sent from my iPhone using Tapatalk

  3. #23
    Join Date
    Feb 2005
    Location
    South of Bawstin
    Posts
    1,281
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Little off the subject here but...

    Do you tie your house keeping pads with rebar into the slab below or do you just "float" them?

  4. #24
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shortcircuit2 View Post
    Little off the subject here but...

    Do you tie your house keeping pads with rebar into the slab below or do you just "float" them?
    Not sure - but I believe it’s preferred to tie them in rather than floating in order to prevent pad from cracking


    Sent from my iPhone using Tapatalk

  5. #25
    Join Date
    Jul 2003
    Location
    MA
    Posts
    2,181
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by shortcircuit2 View Post
    Little off the subject here but...

    Do you tie your house keeping pads with rebar into the slab below or do you just "float" them?
    They are usually installed with dowels drilled into the supporting slab with rebar in the housekeeping pad, but not always.
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices

  6. #26
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tkb View Post
    In 40 years it has never been even a discussion with an inspector on any job that I have seen.
    This is a non issue in New England.

    The OP mentioned a 20” extension. That is too much and should be a violation.
    It should be 3’ to 4’ depending on the condition, or 6”.
    I agree, standard construction.

    Tis a technicality that it is a violation per se, but ignored, similar to objectionable current at a service, necessary evil but allowed.
    "Electricity is really just organized lightning." George Carlin


    Derek

  7. #27
    Join Date
    Jan 2009
    Location
    3 Hr 2 Min from Winged Horses
    Posts
    15,966
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dale001289 View Post
    It’s a judgement call.
    I’ve seen it go both ways - depends on QA/QC inspectors. In Petro-chem facilites they tend to be less tolerant.


    Sent from my iPhone using Tapatalk
    Kinda special area, normal commercial installation usually allows the 6” pad extension.
    "Electricity is really just organized lightning." George Carlin


    Derek

  8. #28
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    41,644
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Carultch View Post
    Can an equipment slab count for the 6" rule per 110.26(A)(3), just as a raceway can penetrate the workspace up to 6"? The article states "other equipment associated with the electrical installation", and a housekeeping slab specifically built for electrical equipment is "associated with the electrical installation".
    I suppose it is a judgement call, I also think most inspectors will consider it to be associated with the electrical installation though. If you didn't have the gear there you wouldn't have that specific slab there.

    Someone messes up and makes it 20" too wide, now you have a problem with working clearances. Make it 36" inches too wide, you may not get what was intended but still possibly comply with working clearances.
    I live for today, I'm just a day behind.

  9. #29
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,531
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jumper View Post
    I agree, standard construction.

    Tis a technicality that it is a violation per se, but ignored, similar to objectionable current at a service, necessary evil but allowed.
    That's what I see. Who really cares if it's a technical violation, we're talking about the floor. I've never seen a pad that wasn't a "violation". In my experience no one really cares about the pad in the working space.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  10. #30
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    That's what I see. Who really cares if it's a technical violation, we're talking about the floor. I've never seen a pad that wasn't a "violation". In my experience no one really cares about the pad in the working space.
    With MV switchgear, you could have an issue with the truck and removal of CB’s.
    6” is not a big deal but beyond that would be


    Sent from my iPhone using Tapatalk