    250.66 vs 250.102(C)(1)

    When sizing an grounding electrode conductor, is anything over 1100cu - "3/0" max required ? Or do you have to do the 12.5% of area as required by 250.102(C)(1)
    " I'm at a crucial part of my painting "...........Monika Danneman

  2. #2
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,804
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ritelec View Post
    When sizing an grounding electrode conductor, is anything over 1100cu - "3/0" max required ? Or do you have to do the 12.5% of area as required by 250.102(C)(1)
    3/0 is max for a GEC. This is the reason that the new Table 250.102(1) was created to attempt to make clear that GEC max out but bonding does not.

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,600
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    That's it, if it's a GEC it's never required to be larger than #3/0. The 12.5% would apply to system bonding jumpers, main bonding jumpers, etc. Our 4000 amp services have the same size GEC as our 225 kva transformers.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Feb 2006
    Location
    Jersey
    Posts
    2,393
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thank you