What is the exact amperage on a 1.5hp, 115volt motor at 90 percent efficiency?


Sent from my SM-N900P using Tapatalk
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
NEC Table 430.248 gives a value of 20 amps. That table does not tell us anything about efficiency. The actual and exact value that you would measure can be anything. It depends on how the manufacturer built the motor, what it is connected to (i.e., its mechanical load), how old the motor is, what its environment is (temperature, humidity, etc.), and a hundred other things.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
What is the exact amperage on a 1.5hp, 115volt motor at 90 percent efficiency?


Sent from my SM-N900P using Tapatalk

The efficiency tells us exactly how much electrical energy is needed to produce a mechanical output of 1.5hp.

But the current will depend on the power factor of the motor, which is not directly determined by the efficiency.
A motor can have a PF of .5 and still have an efficiency of 90% because the reactive current is not delivering any power.
And in fact some changes that make a motor more efficient can also lower the power factor.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What is the exact amperage on a 1.5hp, 115volt motor at 90 percent efficiency?


Sent from my SM-N900P using Tapatalk

What answer did you come up with? Sounds like they were asking you to use the 746 watts/HP calculation.
 

kwired

Electron manager
Location
NE Nebraska
What answer did you come up with? Sounds like they were asking you to use the 746 watts/HP calculation.
Which is fine if they want you to exercise using that formula - they were still short on information to do it though, power factor is also important here.

If multiple choice question maybe answer selections were more obvious to what they wanted?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree the question is vague but since no power factor is given why not assume that it's 1.0?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I agree the question is vague but since no power factor is given why not assume that it's 1.0?
Have you ever seen a single phase AC motor that runs at a PF of 1.0? I haven't. If it's a Shaded Pole motor, the PF could be as low as .6 and if it's a universal motor, it could be as high as .95, so without knowing what kind of motor it is, even guessing is fraught with inaccuracies.

A = kW/VxPFxEff. The test question only gave 2 out of 3 necessary factors. So whatever you come up with will be an estimate, not an exact value.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Have you ever seen a single phase AC motor that runs at a PF of 1.0? I haven't. If it's a Shaded Pole motor, the PF could be as low as .6 and if it's a universal motor, it could be as high as .95, so without knowing what kind of motor it is, even guessing is fraught with inaccuracies.

A = kW/VxPFxEff. The test question only gave 2 out of 3 necessary factors. So whatever you come up with will be an estimate, not an exact value.

No, but sometimes test or practice questions are hypothetical. It doesn't say that the PF isn't 1.0 and does not give another value. The person who wrote the question had something in mind. Assuming that the PF is 1.0 makes the problem workable even if the question is poorly written.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
No, but sometimes test or practice questions are hypothetical. It doesn't say that the PF isn't 1.0 and does not give another value. The person who wrote the question had something in mind. Assuming that the PF is 1.0 makes the problem workable even if the question is poorly written.
Yeah, what was I thinking. Why would someone let reality get in the way of a good test question? :roll:
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
In my opinion, if the motor is single-phase 115 V [60 c/s] rated the rated current it could be:
I=746*HP/Vrated/efficiency/power factor
power factor: 0.66-0.75
then, I=14.4-16.38 A
:)
 