    250.68(C)(2)

    250.68(C)(2) states that 'The metal structural frame of a building shall be permitted to be used as a conductor to interconnect electrodes that are part of the grounding electrode system, or as a grounding electrode conductor.' Does this not mean then that the building steel does not have to be a grounding electrode in order to be a conductor between electrodes? For instance, if I had a steel building that was not in direct contact with the earth for 10 ft. or more couldn't I still go from my service disconnect to the building steel and then 100 ft. away go from my building steel to within 5 ft of where my metal water pipe enters the building and be within the code?

  2. #2
    Join Date
    Jan 2008
    Location
    NC & IN
    Posts
    3,506
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes , well maybe, but you need grd rods, too.. If I read you correctly. Your building steel does not touch the ground. The water line is the superior grd in this case.

    I was originally thinking you were talking about a separate building.
    Last edited by Buck Parrish; 09-16-18 at 02:53 PM.

  3. #3
    Join Date
    Oct 2014
    Location
    Asheville North Carolina
    Posts
    14
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks for the reply. Yes, the water line would be the main grounding electrode and the steel is not connected to the earth. I could then go from the steel to whatever other electrodes are present, correct?