Fail inspection.

Status
Not open for further replies.

michalspike

Senior Member
I failed inspection because no OCP for a new panel.
We relocated panel in a hotel room. 3 other rooms are connected to a same feeders.
120Amp OCP is located in a hotel basement. Do I really need separate OCP for our room?
 

iwire

Moderator
Staff member
Location
Massachusetts
I failed inspection because no OCP for a new panel.
We relocated panel in a hotel room. 3 other rooms are connected to a same feeders.
120Amp OCP is located in a hotel basement. Do I really need separate OCP for our room?

What is the rating of the new panel?
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I would think the panel is a ML and rated at 125.
Unless some local code I would think compliant.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I have main lug panel. Can I install 60 amp breaker in my panel and unscrews lugs.
Will this work?
Yes. You can back feed a 60 amp breaker. Be sure to secure it per 408.36(D).
(I would still suggest you check the length of your taps to assure 240.21 compliance)
 

michalspike

Senior Member
That tap is less then 6 feet.
We have to move panel because of the wall demolition.
Before there was a splice box with taps and panel next to it.
we moved this 6 feet from that space.
Is this change anything if panel itself is 150 Amp rated ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
That tap is less then 6 feet.
We have to move panel because of the wall demolition.
Before there was a splice box with taps and panel next to it.
we moved this 6 feet from that space.
Is this change anything if panel itself is 150 Amp rated ?
If it's a 150 amp panel AND your tap conductors are full size (based on the OCP device protecting them), the install would be legal.

Do you have any idea how I can secure this breaker?
The panel/breaker manufacturer should have a listed device for accomplishing this.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Then, depending on specifics, you would have to terminate at a OCP device rated no more than 70 amps (60 amps if its Romex)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Gus, what makes this a tap and not just a sub from a feeder?
The #6 ! If he had full size (120 amp in his case if I recall correctly) conductors then any sub-panel with a rating that high would be considered to be protected by the (feeder main).
Once he reduced to a #6, that conductor meets the Art 240 definition of a "tap" and must be protected per the 240.21 tap rules.
Did I overlook or misread something ?
 