    Fire Dpt. Says Nat. Gas. Engine Generator Not Emergency

    This came out of left field, but I was informed by my GC that they were told by the fire dpt. that a Natural Gas generator is not considered emergency and only a Diesel generator can be considered emergency.

    I've never heard of this anywhere in any local state or national codes. Mass. Bldg. code clearly does not state this.

    Has anyone ever heard of such a thing?

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,531
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The NEC states allows it when approved by the AHJ. I'm not sure what's changed but up until a few years ago we never installed a natural gas emergency generator.

    700.12(B)(3) Dual Supplies. Prime movers shall not be solely de-
    pendent on a public utility gas system for their fuel supply
    or municipal water supply for their cooling systems. Means
    shall be provided for automatically transferring from one
    fuel supply to another where dual fuel supplies are used.
    Exception: Where acceptable to the authority having ju-
    risdiction, the use of other than on-site fuels shall be per-
    mitted where there is a low probability of a simultaneous
    failure of both the off-site fuel delivery system and power
    from the outside electrical utility company.
    Last edited by infinity; 10-10-18 at 04:09 PM. Reason: Added Code Section
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,678
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    The NEC states allows it when approved by the AHJ. I'm not sure what's changed but up until a few years ago we never installed a natural gas emergency generator.

    700.12(B)(3) Dual Supplies. Prime movers shall not be solely de-
    pendent on a public utility gas system for their fuel supply
    or municipal water supply for their cooling systems. Means
    shall be provided for automatically transferring from one
    fuel supply to another where dual fuel supplies are used.
    Exception: Where acceptable to the authority having ju-
    risdiction, the use of other than on-site fuels shall be per-
    mitted where there is a low probability of a simultaneous
    failure of both the off-site fuel delivery system and power
    from the outside electrical utility company.
    For this reason, you will never find a natural gas fired fire pump. There may be a few in the hinterlands (I personally know of one) but you won't find new installs. Like, the last 20 years or so.

  4. #4
    Join Date
    Jul 2007
    Posts
    473
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    oh boy I'm gonna be bankrupt. I didn't know that

  5. #5
    Join Date
    May 2018
    Location
    Jamaica and london
    Posts
    1,308
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Natural gas lines, supplied by gas companies, can and usually are, shut off when fire departments request it. My cousin is a fireman who has said many times to me that I should not get a gas or natural gas generator as backup for my property because they are both more flammable than diesel. I am not an6 expert but can only say that when it comes to fire hazards, I listen to my cousin...he is the expert.
    Student of electrical codes. Please Take others advice first.

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,531
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    On our last project a 720 unit apartment building with some retail we used a NG generator for all life safety. First time in my career that I've ever seen that.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #7
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,841
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We always get it in writing first from the AHJ before we consider natural gas for 700 or 701 gens.

    I recently had it for a NJ gen and had to provide the letter back to the AHJ during construction and saved my butt
    Ron

  8. #8
    Join Date
    Jun 2017
    Location
    WI, USA
    Posts
    414
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We’ve had NG approved as long as they meet the 10 seconds in some areas of WI.

  9. #9
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    6,678
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Adamjamma View Post
    Natural gas lines, supplied by gas companies, can and usually are, shut off when fire departments request it. My cousin is a fireman who has said many times to me that I should not get a gas or natural gas generator as backup for my property because they are both more flammable than diesel. I am not an6 expert but can only say that when it comes to fire hazards, I listen to my cousin...he is the expert.
    Your cousin is absolutely right. From a flammability risk, diesel is the way to go. The problem for emergency generators is that depending on the load they need to support, you may run into a problem storing enough fuel on site to meet however long it has to run. It may be as little as 24 hours, but in Florida they are requiring nursing homes provide power to run A/C for 96 hours. Most localities won't let you put that much fuel on your property, but natural gas is use it when you need it.

  10. #10
    Join Date
    Jun 2009
    Location
    NW Indiana
    Posts
    405
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Some good points above. I agree with flammability, but I'm a fireman, and I'd want natural gas at my house all day long. Depending on your risk assessment, it would depend on fuel reliability in my mind. Earthquakes are possible here, but most extended outages have been blizzard/ice related that I have experienced. Natural gas interruptions have been extremely rare, and our emergency services building has a natural gas fired generator too. The other issue that has come up over time has been generators with large day tanks having stale fuel issues.