    Bonding Metallic Raceways Connected to Nonmetallic Equipment

    314.3 requires internal (Ex No.1) or integral bonding means (Ex No. 2) when metal raceways or metal-armored cables are used with nonmetallic boxes.

    Why is there no Code requirement for internal or integral bonding means for metal raceways or metal-armored cables used with nonmetallic equipment enclosures?

  2. #2
    Join Date
    May 2018
    Location
    Jamaica and london
    Posts
    1,304
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Even in a non metallic equipment enclosure isn’t there a bonding screw point or grounding screw point? If not, don’t you still treat it like a box, by tying grounds together, including using grounding bushings for metal conduits?
    Student of electrical codes. Please Take others advice first.

  3. #3
    Join Date
    Feb 2005
    Location
    South of Bawstin
    Posts
    1,263
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I don't see any requirement in the Code to bond the metal raceway or metal wiring method to the ground bar inside the nonmetallic equipment enclosure. 314.3 applies to boxes.

    I guess 250.4(A)(5) is the only section I can find that may apply. There would be lower impedance if the metal raceway or metallic wiring method was bonded at the nonmetallic equipment enclosure.