Duplex MC Connectors

Status
Not open for further replies.

lwenzel

Member
Location
Madison, WI
Quick question: When using a duplex MC connector like a 3838ast, is it acceptable to use only one port and leave the other open (only feed one line of MC in)? Does this violate any codes?

Thanks for your help,

Logan
 

jumper

Senior Member
Only thing I found that could fit.

314.17 Conductors Entering Boxes, Conduit Bodies, or
Fittings. Conductors entering boxes, conduit bodies, or fittings
shall be protected from abrasion and shall comply
with 314.17(A) through (D).

(A) Openings to Be Closed. Openings through which conductors
enter shall be closed in an approved manner.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Only thing I found that could fit.

314.17 Conductors Entering Boxes, Conduit Bodies, or
Fittings. Conductors entering boxes, conduit bodies, or fittings
shall be protected from abrasion and shall comply
with 314.17(A) through (D).

(A) Openings to Be Closed. Openings through which conductors
enter shall be closed in an approved manner.

istm an open KO as well. Does anyone make a plug for a 2-1 MC connector with just one MC cable in it?
 

kwired

Electron manager
Location
NE Nebraska
worst case install a very short cable into the connector to plug the hole, but don't connect any of the conductors to anything - is no different then some "spare" being installed for future use.
 