Thread: Are splices required to be performed in a junction box?

  1. #11
    Join Date
    Feb 2013
    Location
    Mississippi
    Posts
    540
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Then there are these:

    Attachment 21585
    Where are these allowed to be used. What code article mentions them.

  2. #12
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    609
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by DBoone View Post
    Where are these allowed to be used. What code article mentions them.
    See post #8

  3. #13
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,183
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Then there are these:

    Attachment 21585
    I've a world of stories about those

    none good...

    ~RJ~

  4. #14
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,775
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    I've a world of stories about those

    none good...
    I've had no issues with them, used the top one mainly to add a receptacle for a TV to an existing circuit.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  5. #15
    Join Date
    Apr 2009
    Location
    Clarkesville, Georgia
    Posts
    2,360
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Then there are these:

    Attachment 21585
    those look better than the ones I've seen

    the ones I've seen had all failed

    took a little while to find
    Dave Ruth

  6. #16
    Join Date
    Feb 2013
    Location
    Mississippi
    Posts
    540
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by readydave8 View Post
    those look better than the ones I've seen

    the ones I've seen had all failed

    took a little while to find
    I previously asked about where to use these

    I believe I will just avoid them now

  7. #17
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    I've had no issues with them, used the top one mainly to add a receptacle for a TV to an existing circuit.
    I've never used the saddle or tap style one.. any tips or tricks with it?

    For the above poster, they are used to splice NM cable in walls without a junction box. Like any other connector, they have their uses ..
    Electricians do it until it Hertz!

  8. #18
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,775
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JFletcher View Post
    I've never used the saddle or tap style one.. any tips or tricks with it?
    Only that the feed-through cable needs to be bent to match the change in level. With all of them, bending the conductors to the correct shape is a must.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  9. #19
    Join Date
    Dec 2018
    Location
    Dalton, MA USA
    Posts
    1
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Open Splices of Class 2 Cct's

    I've been splicing class 2 circuits "open slices" for 38 years. But I really don't know where it says it's okay to do this in the NEC. This has been one of the longest searches I can recall, been to 725, 300 and have found nothing that says it is permitted. I've been teaching for the past 12 years and always tell students to find it in the NEC, but I'm definitely not seeing something!! HELP

  10. #20
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,001
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by larrypark45 View Post
    I have scoured the NEC and cannot find anything except in Temporary wiring that says splices must be performed in a junction box.

    Hopefully one of you code experts can help point me to the right location in this code book to put my mind at rest - and to finish this report!!
    For temporary wiring with NM cable or cords a junction box is not required.

    590.4(G) Splices. On construction sites, a box shall not be required for splices or junction connections where the circuit
    conductors are multiconductor cord or cable assemblies, provided that the equipment grounding continuity is maintained with or without the box. See 110.14(B) and 400.9. A box, conduit body, or terminal fitting having a separately bushed hole for each conductor shall be used wherever a change is made to a conduit or tubing system or a metal-sheathed cable system.
    Rob