Thread: Missing neutral

  1. #41
    Join Date
    Nov 2003
    Location
    The incredible, yet very expensive, Hudson Valley, NY NEC 2014
    Posts
    1,871
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Fmkehoe View Post
    Ulster county. No license needed yet.

    In Ulster county out in the woods there may not have even been a permit pulled.

    Can you post a picture of the whole panel and area? Also a picture of the meter and area.

    Steel well casing bonded?
    Mike, Dutchess County, NY

  2. #42
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    33
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    In the first photo:


    It looks like there is old SE cable coming in the top center hole in the box that has been cut off. What is that? It looks like two old cloth covered AL conductors have been cut off and the bare N/G outer conductor is behind them. Where does that go, and is it bonded to the panel?

  3. #43
    Join Date
    Nov 2003
    Location
    The incredible, yet very expensive, Hudson Valley, NY NEC 2014
    Posts
    1,871
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by robertd View Post
    In the first photo:


    It looks like there is old SE cable coming in the top center hole in the box that has been cut off. What is that? It looks like two old cloth covered AL conductors have been cut off and the bare N/G outer conductor is behind them. Where does that go, and is it bonded to the panel?

    That's one reason why I asked for a picture of the whole panel.
    Mike, Dutchess County, NY

  4. #44
    Join Date
    Aug 2017
    Location
    Cornwall ny USA
    Posts
    113
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Can’t get pics right now but I do know that an addition was put on the house in 1990 so the service was moved to the addition and run new from gable of addition, underground, back to the panel thus the cut old original SE.
    in any event, it’s been working for 28 years