User Tag List
Page 1 of 4 1 2 3 ... LastLast
Results 1 to 10 of 39
Thread: Transformer Issue
  1. #1
    Join Date
    May 2003
    Leesburg, VA
    Posts
    7,108
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Transformer Issue
    I went to a job today to check a ground current issue on a new UPS, they were measuring 15.6 amps on a ground conductor. The UPS is 480/480 3-wire with a factory supplied 480 delta to 208/120 wye 150 kva shielded isolation transformer. So I am told I could not verify the transformer type.
    There is a ground jumper from the frame of the transformer the bottom of a ground bar, from the ground bar there is a bond jumper to a Ground bar in the UPS and then from the ground bar in the UPS there is a bond jumper back to the top of the ground bar in the transformer cabinet. Current seems to be circulating on the from the transformer frame to the UPS ground bar and back to the transformer.
    No load on the secondary, Primary current 15/11/8. With 70% load on the transformer and the ground current went to 22 amps. Utilized a resistive load.
    Results were the same with the UPS on and with the UPS in bypass and the UPS off.
    Removed the top bond jumper in the transformer to the UPS ground bar and current was still on the bottom jumper in the transformer.
    The ground bars are mounted to the metallic frame of the transformer and UPS, so the effect is the same with or without the top ground jumper.
    No measurable current on the grounding electrode conductor, Neutral-Ground Bond or any EGCs
    Any thoughts?
    Brian John
    Leesburg, VA
  2. #2
    Join Date
    Jan 2008
    Posts
    9,666
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Is the UPS connected to supply or checked during isolation? What are voltage readings, phase-phase and phase-ground? What currents do you get with the transformer de-energized?
    BB+/BB=?
  3. #3
    Join Date
    Jan 2008
    Posts
    9,666
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    I noticed you said no EGC currents so that may eliminate common mode signals.
    Check the voltages to see if you might have a partial fault in the transformer. You might meg it also.
    BB+/BB=?
  4. #4
    Join Date
    May 2003
    Leesburg, VA
    Posts
    7,108
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This was brought up on another forum.
    I think the transformer may be an autotransformer
    Not sure the practical reason for an autotransformer for a voltage change of 480 to 208/120? Seems the copper and steel required would be same as a Delta Wye or close.
    Have to think about the XO would that be ground on the primary
    Brian John
    Leesburg, VA
  5. #5
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by brian john View Post
    What is the 480/208 transformer for?
  6. #6
    Join Date
    May 2003
    Leesburg, VA
    Posts
    7,108
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The UPS is 480/480 the transformer feeds the critical loads at 208/120 VAC
    Brian John
    Leesburg, VA
  7. #7
    Join Date
    May 2018
    Ohio
    Posts
    360
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    what are voltage readings. a core may be shorted to a winding
  8. #8
    Join Date
    May 2003
    Leesburg, VA
    Posts
    7,108
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Primary A-B 480, B-C 480, C-A 480
    Secondary A-B 208, B-C 208, C-A 208, A, B, C to N 120
    Brian John
    Leesburg, VA
  9. #9
    Join Date
    Feb 2003
    New York, 40.7514,-73.9925
    Posts
    4,717
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    How is the static bypass fed? Is it 480V and fed to its SS on the primary side of the XFMR or 208V onto the secondary?
    Since you said it was a factory transformer, that why the bypass voltage is important, because as you know there is a N-G bond up at that source that is providing the needed grounding.
    Ron
  10. #10
    Join Date
    May 2003
    Leesburg, VA
    Posts
    7,108
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ron View Post
    The Bypass is on the primary and is 3-wire as well. Isolated the transformer from the UPS, with no connection to the UPS Bypass the issue with the transformer secondary
    still existed
    Brian John
    Leesburg, VA