User Tag List
Results 1 to 6 of 6
Thread: 240V Delta Calcs
  1. #1
    Join Date
    Dec 2018
    Pittsburgh, PA
    Posts
    9
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    240V Delta Calcs
    Hi Everyone,
    First time ever dealing with 240V, 3ph, delta. I'm just curious on the full load amperage calcs - I've got 240V, 3ph panel with 84 kW of load and just wanted to get some verification that the load on the panel would be 84 kW / (240*sqrt(3)) = 202A.
    Thanks in advance!
  2. #2
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    19,439
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Yep. That's right. Welcome to the forum.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  3. #3
    Join Date
    Jul 2006
    SE USA as far as you can go
    Posts
    2,775
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    "Just because you're paranoid, doesn't mean they're not out to get you"
  4. #4
    Join Date
    Jul 2014
    Lancaster, PA
    Posts
    237
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by SDG0413 View Post
    Hi Everyone,
    Thanks in advance!
    Sure, if your load is 100% three phase, you’re good to go. The more single phase there is, the worse the imbalance will be. I’ll never forget amping the conductors at a small Piggly Wiggly. It was an old 400 amp delta service that had seen steady, gradual load growth over 40 years and was running “hot”. Can’t recall the exact numbers but they were something like 430, 440, 150.
  5. #5
    Join Date
    Dec 2018
    Pittsburgh, PA
    Posts
    9
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Iron_Ben View Post
    Geez, I'm sure that system had seen its better days. Thanks for your input!
  6. #6
    Join Date
    Dec 2018
    Pittsburgh, PA
    Posts
    9
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by charlie b View Post
    Much appreciated!
Posting Permissions