    Quote Originally Posted by Adamjamma View Post
    Well, he said 3 phase, 100 amps... so that starts around what, number 2... copper thhn is what I am assuming cooper think means but...of course, now you have the three conductors in a tray or such so you have derating and the 500 feet with 75 degree connections....2/0?.
    If only 3 conductors there is no adjustment necessary. 3AWG is good for 100 amps 75C.

    What is not real clear is if the load is 100 amps or if it a 100 amp feeder with a lesser load on it, as well as what is continuous, what is non continuous for load. Once one knows absolute minimum conductor needed then comes how much voltage drop is acceptable and can the minimum ampacity conductor provide that or not.
    I live for today, I'm just a day behind.

  2. #12
    Join Date
    Jul 2018
    Location
    Indian Land
    Posts
    43
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Question is...
    100a load not continuous. 75 degrees Celsius terminal ratings. 3 phase 480volt supply. 450 feet distance. What size wire should be used?

    Answer is:
    1.732x12.9x100x450/14.4=69,821.25 cmils

    Chapter 9 table 8 ...#1 awg will work ...83,690 cmils. Copper

    Sent from my Moto Z (2) using Tapatalk

  3. #13
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    40,183
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Danny89 View Post
    Question is...
    100a load not continuous. 75 degrees Celsius terminal ratings. 3 phase 480volt supply. 450 feet distance. What size wire should be used?

    Answer is:
    1.732x12.9x100x450/14.4=69,821.25 cmils

    Chapter 9 table 8 ...#1 awg will work ...83,690 cmils. Copper

    Sent from my Moto Z (2) using Tapatalk
    You didn't mention acceptable voltage drop in the question, but apparently is 14.4 volts.
    I live for today, I'm just a day behind.

  4. #14
    Join Date
    Jul 2018
    Location
    Indian Land
    Posts
    43
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    +or- 3%

    Sent from my Moto Z (2) using Tapatalk