Thread: 12 kV conductors from pole to underground transition

  1. #11
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,473
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    The inductance of an isolated conductor carrying AC can be significantly higher than for the same conductor in a three phase bundle, even when there is no ferromagnetic material involved.

    Sent from my XT1585 using Tapatalk
    I guess it comes down to what exactly is meant by "bundle" or "grouped". On one end of the spectrum we could have direct buried conductors that prob ly would be installed the same way in either case. What about iso phase pvc conduits that are right next to each other?
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  2. #12
    Join Date
    Feb 2013
    Location
    India
    Posts
    2,657
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    What about iso phase pvc conduits that are right next to each other?
    Inductance is more when separation distance between iso phase PVC conduits is more and so is voltage drop.

  3. #13
    Join Date
    Nov 2016
    Location
    Dublin, GA
    Posts
    172
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This voltage level is often encountered in large industrial facilities. A typical design would be a three phase pothead on the pole connected to 3/c armored cable for direct burial to a unit substation primary switch.

  4. #14
    Join Date
    Jul 2006
    Location
    SE USA as far as you can go
    Posts
    2,775
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by smarteng View Post
    Hello Sir/Madam

    When transitioning from pole to underground, can we have all 3 phase wire in one conduits or do we need to have one conduit per phase. ( overhead conductor :ACSR, underground : 15KV shielded cable ) Also, whats better practice for underground medium voltage 12 kV line, separate conduit per phase or all cable in one conduit.

    Thank you.
    Depends on who owns the line. If it's the utility you will need to follow there requirements. If it's privately owned then follow NESC.
    "Just because you're paranoid, doesn't mean they're not out to get you"