    Temp String Lights with Cages on the Floor/Slab

    I apologize if I am in the wrong section, I was wondering if there are any OSHA or other safety violations for string lights with plastic cages to be lying on the ground for extended periods.
    Everything not saved will be lost - Nintendo Quit Screen Message

  2. #2
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    1,127
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I’m not looking at the book, but I recall something about temporary wiring esp. nm-b needing to be installed at a height so not to be subject to physical damage. I don’t know if your temp lights also follow this same rule.

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,875
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    590.4(J) is close to what you're asking:

    590.4(J) Support. Cable assemblies and flexible cords and
    cables shall be supported in place at intervals that ensure
    that they will be protected from physical damage. Support
    shall be in the form of staples, cable ties, straps, or similar
    type fittings installed so as not to cause damage. Cable
    assemblies and flexible cords and cables installed as branch
    circuits or feeders shall not be installed on the floor or on
    the ground.
    Extension cords shall not be required to comply
    with 590.4(J). Vegetation shall not be used for support of
    overhead spans of branch circuits or feeders.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    39,705
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    From OSHA perspective sounds like a trip hazard to me, unless you at least place it in a "restricted area".
    I live for today, I'm just a day behind.

  5. #5
    Join Date
    May 2010
    Location
    North of the 65 parallel
    Posts
    2,161
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I do a lot of 590 temporary power. However I have never put temporary lighting down near the floor. Not because I thought I couldn't code wise, but because nobody wants the temp lighting on the floor - they want it up.

    But, if that is what is needed:
    Quote Originally Posted by infinity View Post
    590.4(J) is close to what you're asking:
    Cable assemblies and flexible cords and cables installed as branch
    circuits or feeders shall not be installed on the floor or on
    the ground.
    Infinity is correct - not on the floor. The fix is to lay down 2x4s, 2x6s, 2x(whatever), and staple the cable to the that. Gets it off the floor - meets code.

    Then again, I don't know of any regulation specifically addressing plastic caged light strings
    Without data you’re just another person with an opinion – Edwards Deming