    I have two sets of secondary conductors from 75kva three phase 480v to 208/120v feeding two panels. Each panel main circuit breaker is 225A. So 225x2 = 450a which is 216% of transformer secondary full load amps.
    The primary breaker is sized within 125% of full load amps.
    Customer says transformer is protected by primary breaker. No need for secondary breakers at all in terms of transformer protection. The secondary breakers provided for secondary conductor and in accordance with tap rules. The secondary two sets feeding panels demand load is less than 75kva rating now.
    The demand load of both panels is less than transformer 75kva rating at present but can exceed if in future they add load to panels to exceed that of the 75kva transformer since btoh panels have room and can add in future.
    Is the above allowed in code?
  2. #2
    Join Date
    Feb 2003
    Wisconsin
    Posts
    10,320
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    As described, your installation meets the code requirements of articles 240, 408, and 450.
    Just because you can, doesn't mean you should.
  3. #3
    Join Date
    Jun 2018
    Glen bunie, md, us
    Posts
    490
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jim dungar View Post
    Yes but what about the part where demand load can exceed transformer capacity in future?
    Sent from my SM-G935U using Tapatalk
  4. #4
    Join Date
    Feb 2003
    Wisconsin
    Posts
    10,320
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by hhsting View Post
    The NEC does not address the sizing of transformers.
  5. #5
    Join Date
    Jun 2018
    Glen bunie, md, us
    Posts
    490
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    So any transformer secondary conductors and secondary side panelboard size can be big as one wants, no limit so as long as the nec 2014 articles 450, 240.21 are met?
    Nothing in code to prevent overloading the transformer.
  6. #6
    Join Date
    Feb 2003
    Wisconsin
    Posts
    10,320
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes.
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,277
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It does address overcurrent protection of transformers though. I don't see anything that allows 216% protection of this secondary, I do see it can be 125%, then allows next higher standard size overcurrent device.
    I live for today, I'm just a day behind.
  8. #8
    Join Date
    Feb 2003
    Connecticut
    Posts
    3,534
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    I see that the secondary protection is allowed to be "not required."
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,277
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    OK, note 2 - where secondary protection is required.... where is it required?
    What protects a multiwire secondary should you have severe imbalance if you have primary only protection?
  10. #10
    Join Date
    Feb 2003
    Wisconsin
    Posts
    10,320
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Secondary protection is required when the primary protection exceeds the table value for primary protection only, such as 125% for a 480V primary and 208V secondary.