    Fire rated door contact

    Hello all,

    I have a fire inspector that is fighting me on our door contacts. They are installed in a fire rated steel door, I have been asked to provide a UL listing showing that it is fire rated, or replace it with one that is. I have had no luck confirming the fire rating (I don't believe it is). Below is a link to the UL listing for the current contact.

    http://database.ul.com/cgi-bin/XYV/t...183&sequence=1

    My question is, can anyone recommend a fire rated contact?

    Thanks in advance for your help.

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,592
    Mentioned
    4 Post(s)
    Tagged
    0 Thread(s)
    Not sure what kind you have by check this out

    https://stevenengineering.com/tech_s...C-CONTACTS.pdf

    go to model 1090

    BTW, welcome to the forum
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Dec 2018
    Location
    Bay Area, CA
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thank you, I am not sure this will work for my application, but will help me in the future for sure.

    Any chance anyone was able to find a press fit version?

    And thank you

    Quote Originally Posted by Dennis Alwon View Post
    Not sure what kind you have by check this out

    https://stevenengineering.com/tech_s...C-CONTACTS.pdf

    go to model 1090

    BTW, welcome to the forum

  4. #4
    Join Date
    Sep 2014
    Location
    Nashville, TN
    Posts
    159
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Unless your switch is connected to the fire alarm or a fire alarm device, I'd say your inspector is over-reaching. If not and it needs to be listed, the manufacturer would say so and, more than likely, provide a sample manufacturer and part number.

    I think my concern would be with "modifying" a listed assembly by installing a press-fit contact. I've seen contractors have to "eat" labeled doors because they "modified" them. Rare, but it happens.

  5. #5
    Join Date
    Dec 2005
    Location
    Florida
    Posts
    418
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Rockyb View Post
    Hello all,

    I have a fire inspector that is fighting me on our door contacts. They are installed in a fire rated steel door, I have been asked to provide a UL listing showing that it is fire rated, or replace it with one that is. I have had no luck confirming the fire rating (I don't believe it is). Below is a link to the UL listing for the current contact.

    http://database.ul.com/cgi-bin/XYV/t...183&sequence=1

    My question is, can anyone recommend a fire rated contact?

    Thanks in advance for your help.
    Is he asking for a fire rated doorknob too?

  6. #6
    Join Date
    Dec 2018
    Location
    Bay Area, CA
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I agree with this, the problem is we regularly install both press fit contacts and request to exits on door frames for our access control system. In this case, they questioned the REX, and that led to the contact as well.

    We may be heading towards eating the door frame.


    Quote Originally Posted by GrayHair View Post
    Unless your switch is connected to the fire alarm or a fire alarm device, I'd say your inspector is over-reaching. If not and it needs to be listed, the manufacturer would say so and, more than likely, provide a sample manufacturer and part number.

    I think my concern would be with "modifying" a listed assembly by installing a press-fit contact. I've seen contractors have to "eat" labeled doors because they "modified" them. Rare, but it happens.

  7. #7
    Join Date
    Mar 2003
    Location
    New York
    Posts
    1,859
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Have it welded.
    Contact the people and ask them. TANE ALARM PRODUCTS

  8. #8
    Join Date
    Nov 2008
    Location
    Twin Cities, MN
    Posts
    84
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What does the door frame manufacturer, the RTE motion manufacturer and the door contact manufacturer say about it?

  9. #9
    Join Date
    Dec 2005
    Location
    Florida
    Posts
    418
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Rockyb View Post
    Hello all,

    I have a fire inspector that is fighting me on our door contacts. They are installed in a fire rated steel door, I have been asked to provide a UL listing showing that it is fire rated, or replace it with one that is. I have had no luck confirming the fire rating (I don't believe it is). Below is a link to the UL listing for the current contact.

    http://database.ul.com/cgi-bin/XYV/t...183&sequence=1

    My question is, can anyone recommend a fire rated contact?

    Thanks in advance for your help.
    I thought it was the DOOR that was fire rated? If it has a JB for the security box, then the DOOR was fire rated based on that design. What does the contact have to do with it.?