Use of general lighting fixtures as emergency lighting

Status
Not open for further replies.

victor.cherkashi

Senior Member
Location
NYC, NY
Use of general lighting fixtures as emergency lighting byacquiring the fixtures with integral battery backup option.
The lighting fixture is provided with un-switched hotwire for battery charger directly from circuit breaker in panel.

Some designers say these lighting fixtures must to beun-switched (24/7 on).
Some designers say these lighting fixtures can switchedby any way such lighting relay, wall switch, dimmer, addressable ballast etc.

question: what is correct design?

I very appreciate any link to code requirements.
 

iwire

Moderator
Staff member
Location
Massachusetts
The NEC allows switching them

However even if switched off they must overide any switching during a a power failure.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The NEC allows switching them

However even if switched off they must overide any switching during a a power failure.
Which usually means that the fixture has both a switched control input and an unswitched reference input used for battery charging and to detect power failure.
 

iwire

Moderator
Staff member
Location
Massachusetts
Which usually means that the fixture has both a switched control input and an unswitched reference input used for battery charging and to detect power failure.

Usually.

I was being kind of non-specific because the same rules apply to generator supplied e fixtures.
 