    Switch/Light Wiring

    Just curious as to how others would wire this? So the lights are all on one circuit. So I know you could bring the circuit/power to either the lights or to the switch but normally you would bring the power to the switch. So the F5's are controlled by one switch and the F7 by the other. So you need a separate switch leg from each switch. Would you run (2) 12/2 from each switch? Thanks.
    Attached Images Attached Images  

  2. #2
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,236
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Generally, with cables, 12-2 to switches, 12-2's to each light group, as you said.

    With conduit, J-box above switches, only feed and two legs down, neutral feed through.

    Your switches have a D by each S. Dimmers? Another reason for neutral at switches.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  3. #3
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,354
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    Generally, with cables, 12-2 to switches, 12-2's to each light group, as you said.

    With conduit, J-box above switches, only feed and two legs down, neutral feed through.

    Your switches have a D by each S. Dimmers? Another reason for neutral at switches.
    Yes dimmers.

  4. #4
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    24,236
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It also depends on how the rest of the job is wired; you generally match existing.

    Quote Originally Posted by mstrlucky74 View Post
    Yes dimmers.
    Then I would do one of what I said above, but add a neutral to the conduit.

    Of course, you need a suspended ceiling to use junction boxes.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  5. #5
    Join Date
    Mar 2007
    Location
    Valdosta, GA
    Posts
    4,319
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by mstrlucky74 View Post
    Yes dimmers.
    Is it 0-10v?


    Sent from my iPhone using Tapatalk
    Brought to you by Carl's Jr.

  6. #6
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,354
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by brantmacga View Post
    Is it 0-10v?


    Sent from my iPhone using Tapatalk
    Yes...we use 12/2 with 16/2 mc-pcs cable

    Sent from my SM-N960U using Tapatalk