    Just curious. Furniture in-feeds each 3ckt/6 wire. They show them a direct homeruns for each 3ckt furniture. Would you figure it that way? Why couldn't you combine each of the 3ckt in the ceiling and run one 6ckt homerun back? Thanks.
    Attached Images Attached Images  

  2. #2
    Join Date
    Mar 2007
    Location
    Valdosta, GA
    Posts
    4,500
    Mentioned
    1 Post(s)
    Tagged
    1 Thread(s)
    That’s just showing what you need at each location; how you get it there is up to you. But you’re going to have 6 CCC’s at each box, so if you combine them to one conduit, de-rating factors will apply.

    Each furniture piece is going to have a whip with 3 circuits coming out of it. You just need to put a box at each location with 3 circuits each.

    The last several I’ve done had a carflex whip with one dedicated circuit and one multiwire circuit. Pull a neutral for each to be safe but you may have to go back and install handle ties if yours have multiwire circuits.


    Sent from my iPhone using Tapatalk
    Brought to you by Carl's Jr.

  3. #3
    Join Date
    Sep 2012
    Location
    NJ
    Posts
    2,540
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by brantmacga View Post
    That’s just showing what you need at each location; how you get it there is up to you. But you’re going to have 6 CCC’s at each box, so if you combine them to one conduit, de-rating factors will apply.

    Each furniture piece is going to have a whip with 3 circuits coming out of it. You just need to put a box at each location with 3 circuits each.

    The last several I’ve done had a carflex whip with one dedicated circuit and one multiwire circuit. Pull a neutral for each to be safe but you may have to go back and install handle ties if yours have multiwire circuits.


    Sent from my iPhone using Tapatalk
    Yes, thanks. Stub-up for tele/data and whip from wall box to furniture for both power and tele/data.

  4. #4
    Join Date
    Jul 2005
    Posts
    925
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    That’s just showing what you need at each location; how you get it there is up to you. But you’re going to have 6 CCC’s at each box, so if you combine them to one conduit, de-rating factors will apply.
    ^^this

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •