    400 amp service correct?

    I am contractor on building my own home. I had electrician install a 400 amp service that goes from meter base/shutoff to house that has 2 200 panels. The shutoff at meter base has 2 ground rods 5-6ft apart and 2 ground rods at house panels 5-6ft as well. The bonding strap to neutral
    is hooked up in panels is this correct?






  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,360
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    This is not correct. Does the meter have 2- 200 amp breakers or 1- 400 amp breaker. I assume 2-200 amp breakers which would not be compliant. How many conductors are run from the meter/main to the house. There should be an equipment grounding conductor run with the feeders.

    The meter/main should have the neutral and grounds tied together but not at the house.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Dec 2018
    Location
    Tyler, Texas USA
    Posts
    6
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

  4. #4
    Join Date
    Dec 2018
    Location
    Tyler, Texas USA
    Posts
    6
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    There is a meter can with a 400 amp safety switch fused at pole location then runs to
    house that has 2-200 amp panels with 200 amp breakers

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    40,171
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Does the "meter/shutoff" have overcurrent protection? If not it is not the service disconnecting means and your house panels are the service disconnecting means.

    If it does have overcurrent protection, it still may not be considered the service disconnecting means in some areas, especially if it is POCO provided.

    More details along with knowing what any local rules may be are critical to answering OP's question here.
    I live for today, I'm just a day behind.

  6. #6
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,360
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Chopper143 View Post
    There is a meter can with a 400 amp safety switch fused at pole location then runs to
    house that has 2-200 amp panels with 200 amp breakers

    The closed thread said there were 2 runs back to the house.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  7. #7
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,360
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    You cannot have 2 runs from a single 400 amp breaker going to 2 different panels unless they are joined together and tapped properly.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  8. #8
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,360
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I think you need to get your electrician on here because we are not really allowed to go far with this as you are not the ec.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  9. #9
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    40,171
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Chopper143 View Post
    There is a meter can with a 400 amp safety switch fused at pole location then runs to
    house that has 2-200 amp panels with 200 amp breakers
    Without local rules stating this 400 amp fuse is not the service disconecting means - you would need to run separate neutral and EGC to the house and not bond them together at the house.

    You also need those runs to be "in parallel" to effectively create one feeder to the house, as you can't legally run two feeders to the house. You can make taps off that one feeder to as many as six disconnecting means grouped in same location though.
    I live for today, I'm just a day behind.

  10. #10
    Join Date
    Dec 2018
    Location
    Tyler, Texas USA
    Posts
    6
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Pics of
    meter base
    Attached Images Attached Images  