Hot Dimmers

Status
Not open for further replies.

Adams14

Member
I have been working at a 92 year old church. The dimmer for some two 300 watt incandescent lamps next to the alter, about 100 feet from the 600 watt dimmer are heating up. Will replacing with a 1000 watt dimmer be the cure for the overheating problem?
 

luckylerado

Senior Member
I have been working at a 92 year old church. The dimmer for some two 300 watt incandescent lamps next to the alter, about 100 feet from the 600 watt dimmer are heating up. Will replacing with a 1000 watt dimmer be the cure for the overheating problem?

The heat sync will be larger and do a better job of dissipating the heat but it will still heat up to the touch as this is normal for incandescent dimmers.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The heat sync will be larger and do a better job of dissipating the heat but it will still heat up to the touch as this is normal for incandescent dimmers.
To the extent that the 1000W dimmer uses larger semiconductor elements with lower internal resistance the power dissipated at the same load will be somewhat lower.
If all the 1000W dimmer does is improve the heat sink you will be pushing out the same amount of waste heat but at a lower temperature.
 

JFletcher

Senior Member
Location
Williamsburg, VA
A 600W dimmer is maxed out by 2 300W bulbs. Yes, it will be warm/hot to the touch. Even if you go with different, lower wattage lamps, check the dimmer - all it takes it for one to overheat/run hot once to start self destructing. The last 1000W models I looked at had a rather large faceplate heatsink and were 3-5x the cost of a 600W dimmer, but they will last.
 
Status
Not open for further replies.
Top