    Is the frame of a generator set up as an SDS required to have it's own GEC run to the building GES? The generator frame has 4 switches mounted directly to it with bonded neutrals and each with a separate GEC run to the GES.
    Rob
  2. #2
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,936
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    We've had this question come up a number of times. I'm assuming you have the typical outdoor genset that many would say is a separate structure and thus not require the 2 GES be bonded together. I not sure the code directly addresses this but I will say that it is a pretty common situation since we rarely see gensets inside the structure it is serving anymore. I'm inclined to say that the 2 GES should be bonded together.
  3. #3
    Join Date
    Feb 2003
    Illinois
    Posts
    24,137
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I see no reason to run a GEC between the generator and the building, but an EGC, or in some cases a supply side bonding jumper will be required between the two locations and that will bond the two grounding electrode systems together.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,320
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I should have mentioned this is a generator within a room in the building. There is a large lug on the frame that says "ground", we're being told to run a GEC to that lug I was just wondering why it's needed. Could it simply be due to manufacutrer's instructions?
    Rob
  5. #5
    Join Date
    Mar 2003
    Vermont
    Posts
    2,473
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I don't see anything in 445 other than 445.20(A)(B)
    As an aside , we recently mitigated a few gfci ocpd's tripping on transfere , by simply lifting the genset bond 'floating' the noodle.
    ~RJ~
  6. #6
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    8,175
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The lug "ground" requirement is done by the manufacturer, they typically don't have an understanding of the NEC. Mike Holt went round and round with Generac over this issue. Our AHJs required a connection to the lug under 110.3(B).
    Moderator-Washington State
    Ancora Imparo
  7. #7
    Join Date
    Nov 2010
    Posts
    2,936
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Given that it is in the same building and connected as a SDS then its GES would need to connected to the building GES and with your experience I'm sure you get that. I think being a SDS that "ground" lug becomes moot.