User Tag List
Results 1 to 10 of 10
Thread: Out building feed from house
  1. #1
    Join Date
    Mar 2015
    Tucker, GA
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    We have an existing 60 amp single phase 3 wire UF cable from house panel.
    Is it correct to drive new grounding electrodes and not bonding neutral?
  2. #2
    Join Date
    Dec 2010
    Tennessee NEC:2017
    Posts
    5,048
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Welcome to the forum!
    It depends on what you are calling a "3-wire" cable. If you mean 3-wire plus ground (EGC) then yes, you need a GEC and separate neutrals/grounds. Also, the GEC has to land on the EGC bar.
    If you mean 3-wires total, and if this is a new install, it's not allowed anymore. You would need the "4th" wire. In times past you could run the cable without ground (depending on circumstances such as no waterlines or other metallic paths between buildings) then bond the neutral to the cabinet along with the GEC.
    If you aim at nothing, you will hit it every time!
  3. #3
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,194
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    assuming 240/120 and 3 wire with ground.. yes
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,613
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jp480volt View Post
    Depends on what you mean by existing and if it's only 3 conductors. Prior to the 2008 NEC it was permitted to bond the neutral at a separate structure when that structure met a few conditions. If those conditions are met and it's prior to the adoption of the 2008 you can leave it and install a GES.
    Rob
  5. #5
    Join Date
    Mar 2015
    Tucker, GA
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Little Bill View Post
    3-wire= (2-hots, 1-neutral NO EGC) wire is existing wire. Feeds well pump and lights.
    This shows neutral grounded again.
  6. #6
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,138
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    The ground rod, equipment grounding conductor's and neutrals must all be bonded together in the panel at the outbuilding.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  7. #7
    Join Date
    Mar 2003
    Vermont
    Posts
    1,950
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This must be some ancient UF.....~RJ~
  8. #8
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,041
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    Not necessarily. As mentioned, the code changed in 2008, and many jurisdictions lag years behind. For example NY is still on 2014.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  9. #9
    Join Date
    Feb 2003
    Fl
    Posts
    17,479
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    I think Steve was referring to the UF without an EGC. I used 10/3 NM without an EGC in the late 70's early 80's for dryers.
    Roger
    Join Date
    Jun 2004
    Posts
    5,041
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by roger View Post
    Roger
    oh ok, missed that post.
Posting Permissions