    Out building feed from house

    We have an existing 60 amp single phase 3 wire UF cable from house panel.
    Is it correct to drive new grounding electrodes and not bonding neutral?

  2. #2
    Join Date
    Dec 2010
    Location
    Tennessee NEC:2017
    Posts
    5,104
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Welcome to the forum!

    It depends on what you are calling a "3-wire" cable. If you mean 3-wire plus ground (EGC) then yes, you need a GEC and separate neutrals/grounds. Also, the GEC has to land on the EGC bar.

    If you mean 3-wires total, and if this is a new install, it's not allowed anymore. You would need the "4th" wire. In times past you could run the cable without ground (depending on circumstances such as no waterlines or other metallic paths between buildings) then bond the neutral to the cabinet along with the GEC.
    If you aim at nothing, you will hit it every time!

  3. #3
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,441
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    assuming 240/120 and 3 wire with ground.. yes
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,988
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jp480volt View Post
    We have an existing 60 amp single phase 3 wire UF cable from house panel.
    Is it correct to drive new grounding electrodes and not bonding neutral?
    Depends on what you mean by existing and if it's only 3 conductors. Prior to the 2008 NEC it was permitted to bond the neutral at a separate structure when that structure met a few conditions. If those conditions are met and it's prior to the adoption of the 2008 you can leave it and install a GES.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    Mar 2015
    Location
    Tucker, GA
    Posts
    3
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Little Bill View Post
    Welcome to the forum!

    It depends on what you are calling a "3-wire" cable. If you mean 3-wire plus ground (EGC) then yes, you need a GEC and separate neutrals/grounds. Also, the GEC has to land on the EGC bar.

    If you mean 3-wires total, and if this is a new install, it's not allowed anymore. You would need the "4th" wire. In times past you could run the cable without ground (depending on circumstances such as no waterlines or other metallic paths between buildings) then bond the neutral to the cabinet along with the GEC.
    3-wire= (2-hots, 1-neutral NO EGC) wire is existing wire. Feeds well pump and lights.

    This shows neutral grounded again.

  6. #6
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,358
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jp480volt View Post
    3-wire= (2-hots, 1-neutral NO EGC) wire is existing wire. Feeds well pump and lights.

    This shows neutral grounded again.
    The ground rod, equipment grounding conductor's and neutrals must all be bonded together in the panel at the outbuilding.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  7. #7
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,172
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    This must be some ancient UF.....~RJ~

  8. #8
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,333
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by romex jockey View Post
    This must be some ancient UF.....~RJ~
    Not necessarily. As mentioned, the code changed in 2008, and many jurisdictions lag years behind. For example NY is still on 2014.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  9. #9
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,556
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Not necessarily. As mentioned, the code changed in 2008, and many jurisdictions lag years behind. For example NY is still on 2014.
    I think Steve was referring to the UF without an EGC. I used 10/3 NM without an EGC in the late 70's early 80's for dryers.

    Roger
    Moderator

  10. #10
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    5,333
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by roger View Post
    I think Steve was referring to the UF without an EGC. I used 10/3 NM without an EGC in the late 70's early 80's for dryers.

    Roger
    oh ok, missed that post.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •