    Quote Originally Posted by K8MHZ View Post
    314.23(2)(D) actually allows for enclosures to be mounted to structural or supporting elements of suspended ceilings, provided they meet the mounting requirements of the rest of the section.

    I see no provisions on the box at all for mounting. Maybe that's enough to gig the box on it's own.
    It has a tab for attaching drop wire similar to some recess light housings for support.

  3. #53
    Join Date
    Dec 2005
    Location
    Florida
    Posts
    283
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by K8MHZ View Post
    Yeah, humans are the worst.

    C'mon....73's and 88's

  4. #54
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    10,369
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mopowr steve View Post
    It has a tab for attaching drop wire similar to some recess light housings for support.
    300.11 (A) "Support wires that do not provide secure support shall not be permitted as the sole support"
    Cheers and Stay Safe,

    Marky the Sparky

  5. #55
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    10,369
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Gary11734 View Post
    C'mon....73's and 88's
    73, but no 88's for you.
    Cheers and Stay Safe,

    Marky the Sparky

  6. #56
    Join Date
    Dec 2005
    Location
    Florida
    Posts
    283
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by K8MHZ View Post
    73, but no 88's for you.

    Hay, As General Patton, said to Montgomery; I shaved real close today to be smacked by you! lol

  7. #57
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    1,098
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by K8MHZ View Post
    300.11 (A) "Support wires that do not provide secure support shall not be permitted as the sole support"
    In conjunction to the support wire, the box also relies on the T grid as support just like any other fixture.

    tit for tat

  8. #58
    Join Date
    Dec 2005
    Location
    Florida
    Posts
    283
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mopowr steve View Post
    In conjunction to the support wire, the box also relies on the T grid as support just like any other fixture.

    tit for tat
    There is no doubt in my mind, Mopowr wants to use this in a future installation!

    Hey, its great, just don't put more than 49 volts in it and you are golden...

  9. #59
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    1,098
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Gary11734 View Post
    There is no doubt in my mind, Mopowr wants to use this in a future installation!

    Hey, its great, just don't put more than 49 volts in it and you are golden...

    Yes, I would like the opportunity to be able to use this type of box if the condition arises. But only if it’s listed to be used in this fashion that’s described in product description. Now honestly I would probably use the box as an end of run for the connection to some fixture so not to have a bunch of wires in there. And as a caring electrician I would be diligent in how connection were made within that box so not to energize the grid. I do agree that the box should have a friction fitting clip of sorts to provide solid Bonding of the track.

    I believe the video is done by a sales rep not necessarily an engineer that patented the design and submitted for NRTL listing if that has been done. But I have not yet confirmed that neither.

  10. #60
    Join Date
    Jun 2012
    Location
    NW Ohio
    Posts
    1,098
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    2-1/8 in deep, 4 in octagon boxes with back side tie wire tabs and (4) side T-bar slots and (2) 1/2 in Bottom knockouts are used to install ceiling lighting fixtures, fans, convenience junction boxes and devices.

    contradicting statements between video and product description