User Tag List
Page 1 of 7 1 2 3 ... LastLast
Results 1 to 10 of 64
Thread: SPD to protect GFCIs
  1. #1
    Join Date
    Nov 2018
    new york
    Posts
    280
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    To vendors, electricians, engineers,
    For a house with 10 GFCI receptacles, they would be useless if the GFCIs got fried by external surges. The internal MOV (Metal Oxide Varistors) in each is not enough. They are good for only a few years then the GFCI circuit become vulnerable to damage.
    Now consider this Siemens whole house 140,000A surge current SPD (Surge Protector Device) with data sheet at:
    https://www.downloads.siemens.com/do...id1=BTLV_43434
    available at amazon https://www.amazon.com/gp/product/B0...k_ql_qh_dp_hza
    The wires are only size #10 AWG and it requires 20A breaker.
    What would happen if this is connected to the main breaker of say 100A instead of buying 16 pieces and connecting to each 20A breaker.
    Note it is not an appliance. It doesn't conduct at normal voltage. Only when it reaches above the threshold voltage (MCOV rating) that it begins to conduct and do the voltage divider impedance action thing. But notice that this voltage divider action is only for the surges, not the normal 100A current.
    So my question is whether Siemens requiring it to put on each 20A breaker and buy 16 pieces is just sales gimmick instead of buying just one to put on the main 100A breaker.
    Can the 100A regular current really passes through the Siemens SPD when the SPD only conducts at higher voltage during actual surges. Even then, the voltage divider action is for only for the surge current and not the regular 100A, is it?
    Btw.. let's not confuse the 140,000A surge current rating which is the capacity of the Surge current the SPD can handle, not the regular current (note too that Siemens knows their #10 awg can handle 140,000A surge current because it is not continuous.. so what's wrong putting it in 100A breaker instead of buying 16 pieces for each 20A breakers?).
    If you want to protect all the 10 GFCI receptacles at the house, what kind of main breaker SPD do you usually use? Do you really need the SPD to have #2 AWG wire. Notice an SPD is not normal load or appliance so why does the wiring have to match the regular wiring and ampere table?
  2. #2
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,262
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by tersh View Post
    You're only supposed to add one 2p breaker to the panel that supplies only the SPD and it protects every circuit in the panel.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  3. #3
    Join Date
    Nov 2018
    new york
    Posts
    280
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by LarryFine View Post
    I know. I was asking what if the 2p breaker is the 100A main breaker instead of a branch only. Putting it in the main breaker can protect the entire house. If you put it in each branch, it should only protect the circuits connected to that breaker branch only (edit: unless you mean by connecting it to one branch breaker (say 20A) only, it can protect the other 15 breakers too??)
  4. #4
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,262
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Not correct. Even on its own breaker, it protects all circuits. It's not supposed to be connected to an existing breaker that supplies other wires.
    Larry B. Fine
    Master Electrician
    Richmond, VA
  5. #5
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,811
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The OP has a serious misunderstanding of the fundamentals of surge protection. Not only will it not make any difference if it is connected to a branch breaker or the main breaker, it would also violate the listing as it says it must be connected to a 20 amp OCPD.
  6. #6
    Join Date
    Nov 2018
    new york
    Posts
    280
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I added the edit a few seconds later in message 2. So by connecting it to one branch breaker (say 20A) only, it can protect the other 15 breakers too and their circuits or all loads in the entire house??
    Never realized this before although I owned another Siemens Whole House 140,000A SPD and put it in another building.
    I'll share this info to millions of households in my country, so I guess I make amazon a million dollar richer, lol. Thanks.
  7. #7
    Join Date
    Nov 2018
    new york
    Posts
    280
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If it's connected to an existing 30A breaker that supplies other wires and load, and the ampere of the load is only 10A or less, the Siemens connected to it would still protect the load in that shared breaker.. isn't it?
    No problem reserving a dedicated breaker to it. I thought the past 6 months it only protects the breaker it is connected too.
  8. #8
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,262
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes, but you should use an additional 20a 2p breaker, not one already in use supplying a load.
    Larry B. Fine
    Master Electrician
    Richmond, VA
  9. #9
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,262
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Not exactly; it shouldn't share a breaker. The SPD doesn't draw 20a, that's just the size breaker that should be used.
    Nope, all of them. Parallel is parallel.
    Larry B. Fine
    Master Electrician
    Richmond, VA
  10. #10
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,425
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This is to be used on a grounded system with a neutral conductor at the panel where it is used, not just earthed.
    Tom
    TBLO
Posting Permissions