User Tag List

Results 1 to 7 of 7

Thread: Annex C in the 2017 do you add one for equipment grounding conductor

  1. #1
    Join Date
    Jan 2019
    Location
    Baytown Tx
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Annex C in the 2017 do you add one for equipment grounding conductor

    I am studying for an exam and one of the questions is....
    What is the maximum number of size 12 AWG THHN conductors permitted to be installed in a trade size 3/8 in flexible metal conduit where the fittings are outside the FMC .
    Annex C.3 gives an answer of 3 conductors.
    The answer sheet tells me to add one conductor for equipment grounding conductor, so that makes the answer 4
    Is this correct?

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,988
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Look at Table 348.22 Maximum Number of Insulated Conductors in Metric Designator 12 (Trade Size 3 ⁄ 8 ) Flexible Metal Conduit (FMC) the asterisk at the bottom.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Jun 2015
    Location
    NYC, NY
    Posts
    218
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Footnote under table. *In addition, one insulated, covered, or bare equipment grounding conductor of the same size shall be permitted.

    Sent from my ONEPLUS A6013 using Tapatalk

  4. #4
    Join Date
    Jan 2019
    Location
    Baytown Tx
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Annex C

    Thanks for all your help I was using the wrong table.

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,988
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Chuck 1961 View Post
    Thanks for all your help I was using the wrong table.
    Yes that one is tricky because you need to look at Article 348 for FMC not just the fill in Annex C. I've taken several licensing exams and that question seems to be on every one.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Jan 2019
    Location
    Baytown Tx
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Thanks

    Thank you infinity for clearing that up for me. It was definitely a tricky one that I will remember. Thanks and God Bless!

  7. #7
    Join Date
    Jan 2019
    Location
    Baytown Tx
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Thanks

    Thanks to Victor as well! You guys are the best!