    Quote Originally Posted by david luchini View Post
    They divide the transformer rated secondary current by the percent impedance...But since the percent impedance can have a 10% tolerance, the use the low side of 0.9%Z, which would give the highest possible short circuit value.
    208.19A/0.9%=23132A
    How do you figure out the percent impedance is 10%Z and use the low side of 9%Z
  2. #12
    Join Date
    Nov 2007
    Posts
    958
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by BatmanisWatching1987 View Post
    When the utility gave you the available short-circuit value of 27kA at the transformer terminals, it means the %Z being considered was FLA/Isc = 624A/27,000A = 2.31%!
  3. #13
    Join Date
    Feb 2003
    Connecticut
    Posts
    3,440
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I'm not sure what you are asking. The table that you referenced lists 1%Z for the 75kva transformer.
    1%Z +10% gives a range of 0.9%Z to 1.1%Z.
  4. #14
    Join Date
    Jul 2006
    SE USA as far as you can go
    Posts
    2,775
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The short circuit value wouldn't utilize a tolerance from the utility. They know what the transformer impedance is, or is going to be. The tolerance is only used by manufacturing to IEEE standards.
    A utility transformer with an impedance of 2.31% is very realistic.
    "Just because you're paranoid, doesn't mean they're not out to get you"
  5. #15
    Join Date
    Jul 2007
    Posts
    430
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Is the transformer primary voltage relevant?
    Thanks
  6. #16
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,441
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    IMO, once the utility gives you the available current at their transformer terminals, the transformer, impedance, etc. become irrelevant. All you need is their number.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  7. #17
    Join Date
    Jul 2006
    Posts
    2,775
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
  8. #18
    Join Date
    Jan 2019
    NJ
    Posts
    43
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    You have all the information you need to use the Bussmann app for this calculation. You just start with "add a conductor" to my system.
    Using your information in the app, and assuming steel conduit, I get 17,191 amps at the end of your 100' run.
    I'm not sure what I am doing incorrectly?
    I selected "No, Assume Infinite Current on Primary"
    What was the Z% value you inputted into the system
    Or did I fill out the conductor information incorrectly.
    Click image for larger version.
    Also if I wanted to add my MDP at the end of the line, why does it ask for distance again when inputting a Bus Run to the system?
  9. #19
    Join Date
    Feb 2003
    Connecticut
    Posts
    3,440
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Forget the part about a transformer. Start your calculation with "Add conductor run to system."
  10. #20
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,441
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    same