User Tag List
Results 1 to 9 of 9
Thread: Pavers Around Pool
  1. #1
    Join Date
    Jun 2012
    Oregon, US
    Posts
    68
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Pavers Around Pool
    We have a pool that is surrounded by 2" stone pavers. There will be a 6" rat slab underneath with 1" mortar under the pavers. The contractor just informed me that there will not be rebar in the concrete. If I run a #8 bare inside the grout does this fulfill the epuipotential bonding?
  2. #2
    Join Date
    Mar 2003
    Vermont
    Posts
    2,473
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    good Q
    If i had my way, i'd be in before the pavers with wire mesh......~RJ~
  3. #3
    Join Date
    Jun 2003
    Hawthorne, New York NEC: 2014
    Posts
    4,694
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Well, see it doesn't work that way. YOU tell HIM that there needs to be unless he wants break it all up and do it over when it doesn't pass inspection.
    -Hal
  4. #4
    Join Date
    Mar 2014
    Park Ridge, NJ
    Posts
    155
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Need to run the bond wire before the pavers. Inspectors can be picky about depth requirement below the surface. Also the distance from the pool water.
    From a concrete construction standpoint, the 6" slab should at least be reinforced with wire mesh, which must be bonded.
    Is this a vinyl pool or concrete? New construction or reno?
  5. #5
    Join Date
    Jun 2012
    Oregon, US
    Posts
    68
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    They are planning on using fibermesh which is basically little fiberglass hairs that are mixed into the concrete.
  6. #6
    Join Date
    Apr 2003
    Fort Collins, Colorado
    Posts
    1,761
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You have to comply with 680.26(B)(2). IMO
    Ron
  7. #7
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by NorthwestPV View Post
    I don't think there is any requirement for rebar in the concrete. It will likely require some kind of reinforcement in the concrete to keep it from cracking but it does not have to be rebar.
    It seems to me that a #8 bare copper wire meets the requirements if installed IAW the code requirements for such things.
    I am not real sure the pool bonding requirements actually serve as much of a useful purpose as one might hope, but they are what is required.
    Bob
  8. #8
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,422
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    for such a thin layer of concrete this will probably work better than mesh or rebar anyway.
    Bob
  9. #9
    Join Date
    Mar 2014
    Park Ridge, NJ
    Posts
    155
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes, familiar with the fibermesh. I'm just old school I guess and prefer steel reinforcement especially beyond a 4" thickness.
Posting Permissions
  • You may not post replies
  • You may not edit your posts