Thread: Bond Bushings, when necessary?

  1. #1
    Join Date
    Mar 2015
    Location
    CA
    Posts
    39
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Bond Bushings, when necessary?

    So I've always been trained to use bond bushings if there is a koncentric knock out and not all of it has been knocked out, and every raceway entering a transformer (standard transformer install, nothing out of the ordinary). I see in the code book about the koncentric knock out's, but are they really needed in transformers? Can't a regular plastic bushing be used?

    Thanks

  2. #2
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    2,366
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    w/o looking, service entrance ,SDS's, and 480v work....~RJ~

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,234
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jonny1982 View Post
    So I've always been trained to use bond bushings if there is a concentric knock out and not all of it has been knocked out, and every raceway entering a transformer (standard transformer install, nothing out of the ordinary). I see in the code book about the concentric knock out's, but are they really needed in transformers? Can't a regular plastic bushing be used?

    Thanks
    Concentric knock out-maybe depending on voltage or other factors.
    Every raceway entering a transformer-almost always not required except on GEC in a metal raceway
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    20,230
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Concentric knock out-maybe depending on voltage or other factors.
    Every raceway entering a transformer-almost always not required except on GEC in a metal raceway
    That is actually GEC in a ferrous metal raceway (i.e magnetic), not that aluminum or stainless are all that common.

  5. #5
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    16,578
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It's definitely one of those scenarios where the devil is in the detail. Type of raceway, voltages, concentric & eccentric knockouts and GEC or not all play a part not to mention some inspector's outlook. For that reason, some folks just adopt an attitude of "use one regardless".
    In your case the type raceway (ferrous vs non-ferrous, flex vs hard pipe) and the voltage of the conductors will play a part,
    Generally speaking, < 250 volts-to-ground, a bond bush is likely not needed; >250v to ground, one well might be
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,234
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by GoldDigger View Post
    That is actually GEC in a ferrous metal raceway (i.e magnetic), not that aluminum or stainless are all that common.
    Yes I should have said magnetic raceway (although the NEC doesn't). Stainless steel can still be a ferrous metal.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #7
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,463
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by jonny1982 View Post
    So I've always been trained to use bond bushings if there is a koncentric knock out and not all of it has been knocked out, and every raceway entering a transformer (standard transformer install, nothing out of the ordinary). I see in the code book about the koncentric knock out's, but are they really needed in transformers? Can't a regular plastic bushing be used?

    Thanks
    Service raceways and raceways with GEC's inside them are special cases that require them, where they otherwise would not be required. Service raceways would require at least one, GEC ferrous raceways require them on both ends. No special raceway bonding requirements for either the primary or secondary of the circuits connected to customer-owned transformers. The secondary conductors of a utility-owned transformer, are service conductors, and would require the bonding bushing for that reason.

    As for the general case, it depends on if standard locknuts can get you proper electrical bonding to the enclosure. The over 250V nominal to ground threshold is specified that when ring knockouts remain, you cannot rely on the narrow metal connections between ring KOs to have sufficient continuity, and thus need a bonding bushing/jumper to provide an additional path. That is, unless the enclosure is otherwise listed for standard locknut bonding through the knockout at the voltage in question (and it will be a much more heavy duty knockout than a typical knockout). Nonmetal enclosures for obvious reasons, cannot bond the raceway to the enclosure wall, and therefore would require a bonding bushing if either not properly bonded on the other end, or you use the raceway as the EGC (instead of a separate wire).

    Twice the voltage feeding a fault, means four times the power generated in a chokepoint like a ring KO connection. That is why higher voltages drive this requirement.
    Last edited by Carultch; 01-10-19 at 10:33 PM.

  8. #8
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    27,234
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    In many applications other devices such as bonding locknuts or bonding wedges can be used instead of bonding bushings where standard locknuts are not sufficient for bonding. Service raceways would be one example.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted